Outer covering on large conductors?
#1
Member
Thread Starter
Join Date: Jan 2019
Posts: 67
Received 0 Votes
on
0 Posts
Outer covering on large conductors?
Do larger guage wire have a protective outer layer over the insulation like you see on regular thhn/thwn wire? (im refering to the clear (thermoplastic?) outer layer that gets nicked up when you pull wire).
I have service entrance conductors that look split. 3 individual conductors not a cable, I assume 8awg or 6awg. They are only a few years old. I dont see bare copper though under the split and it looks an outer later is curling in the sun or was split/nicked when pulling.
unfortunately my photo is poor.
I have service entrance conductors that look split. 3 individual conductors not a cable, I assume 8awg or 6awg. They are only a few years old. I dont see bare copper though under the split and it looks an outer later is curling in the sun or was split/nicked when pulling.
unfortunately my photo is poor.
#2
Sometimes they do, sometimes they don't. The conductors the power company use tend to not have a nylon sheath, but the polyethylene insulation is quite thick and durable. If the electrician who installed your service used THHN there will be a nylon sheath, but if they used XHHW or USE there likely won't be. From what I can see in the pictures, your service drop and drip loops look normal and are in OK condition.