when do I need a 100k AIC?

I see some load centers are rated at 100kA and some at 22k. When is the higher required?
 
Sponsored Links
  #2  
Old 06-10-19, 12:57 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,866
Likes Received: 22
It's based on the size of the upstream utility transformer, fuses and possibly the cabling in between (calculated as a fuse). The AIC should be greater than the highest possible fault current coming in the service lines. Residential stuff should all be OK at 22kA, but commercial sites or multi-tenant might need higher AIC and/or coordination with upstream fusing at the main service entrance.
 
  #3  
Old 06-11-19, 08:40 AM
Member
Thread Starter
Join Date: Oct 2005
Location: USA
Posts: 1,240
Likes Received: 1
I have a quite short overhead drop of maybe 25 foot to a 50kVA pole transformer.
I don't want to do a new load center at my house that will be rejected.
I'll talk to a distribution guy at the POCO.
 