Subpanel: getting from here to there

Reply

  #1  
Old 06-24-19, 03:53 PM
F
Member
Thread Starter
Join Date: Jun 2019
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
Subpanel: getting from here to there

I want to upgrade the power to a detached garage. The challenge is getting from the breaker box to the place where the (nice, big) buried conduit leaves the house. The wiring now runs through the walls, and that's not an option.

It's a southwestern style house with flat roofs. The only thing I see is to run up the wall from the box, punch through parapet, wander a bit (some intermediate height changes and walls),, then come out through the parapet and down the wall at the other end.

So, can I use SER cable? Because (a) it has to bend sharply to get through the parapet, and (b) if it has to transition to individual wires before the conduit, how can I do that? This is for 100A service in sunny Arizona.
 
Sponsored Links
  #2  
Old 06-24-19, 04:37 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,434
Received 93 Votes on 73 Posts
1-1-1-3 Al SER can be used for 100A and you will need a large junction box at end of conduit to splice to the individual wires that will go through the conduit.
 
  #3  
Old 06-25-19, 04:38 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,730
Received 65 Votes on 61 Posts
Hi, how do plan on securing the SER? a pic of the roof area might be helpful.
Geo
 
  #4  
Old 06-25-19, 12:48 PM
D
Member
Join Date: Jan 2019
Location: Southern Arizona
Posts: 118
Received 3 Votes on 3 Posts
I do not believe SER is rated to be in the sun.
The farther away the load the bigger the wire has to be.
Then there is the derate factors which sunny days in Arizona are going to be needed. When I did wiring in the Phoenix area I would purchase 90C wire and use the 60C table. If you chose #1 Al the 90C load is 115 amps and the 60C load is 85 amps. You need to know the distance and load to choose a conductor.
Lastly there is the making the roof waterproof again. I spent 30 years in Phoenix doing electrical work. I did 3 flat roofs, the best way I knew. They all leaked. I never did another flat roof again.
Have you considered underground around the perimeter of you structure?
 
  #5  
Old 06-25-19, 03:31 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,434
Received 93 Votes on 73 Posts
SER is sunlight resistant.
https://www.mysouthwire.com/medias/s...4083371038.pdf
 
CasualJoe voted this post useful.
  #6  
Old 06-27-19, 10:24 PM
F
Member
Thread Starter
Join Date: Jun 2019
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
I've never dealt with aluminum wire and had been figuring on copper, probably around 3-3-3-5. Also, I'd been figuring this out for individual wires in conduit, but don't want to miss out if SER is better. (Better meaning easier, cheaper, or both.)

There would be no holes in the roof. The cable or conduit would go up the wall, punch through, then run along the inside of the parapet above the roof. High enough above it there's no watertightness issue. Burying...no, that won't work. There's too much stuff buried there already.
 
  #7  
Old 06-28-19, 05:11 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
SER is easier to install, and a little cheaper, but conductors in conduit is more durable. Either is OK by code so it's your choice. I would probably use EMT conduit along the building walls and parapet with THHN wires pulled in. This method could also eliminate the splice box if you gauge the pull correctly.
 
  #8  
Old 06-28-19, 05:24 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,730
Received 65 Votes on 61 Posts
Hi, THWN for wet locations, I believe.
Geo
 
  #9  
Old 06-28-19, 05:38 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
True, but they are essentially the same thing nowdays as all commonly available THHN also carries a THWN-2 rating. Southwire, Cerrowire, General Cable, for example all list THHN and THWN-2 as the same product in their catalogs.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: