Another circuit-to-shed question

I have a spare 20a breaker in my main house box. I would like to run a cable from the breaker to an outside jct outlet box and continue that to my shed 60ft away. When I get to the shed, i would like to have 2 jct boxes, one for a feed to an underground sump pump near the shed, the other to a combo plug/light switch (prob never use more than 15a).

Can I do this with a 12/2 feed to the outside box, then a 12/2 UF wire to the shed? Bury 18" deep? Would a single GFI outlet at the outside box suffice for ground fault?
 
Sponsored Links
  #2  
Old 06-27-19, 08:52 AM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,132
Upvotes: 0
Received 19 Votes on 16 Posts
What is the amp requirement of the sump pump? If 120V, 20A the bury depth is 12" provided the circuit is fed from a GFCI outlet or breaker back at the house.
 
  #3  
Old 06-28-19, 07:26 AM
maarkr's Avatar
Member
Thread Starter
Join Date: Mar 2014
Location: United States
Posts: 291
Received 4 Votes on 2 Posts
yes, sorry, I plan to use a 120v 20a max sump.

so i take it the single circuit with 12/2 is good to go? thanks
 