Building a kitchen island. Running electrical conduit.


  #1  
Old 06-28-19, 01:56 PM
M
Member
Thread Starter
Join Date: May 2019
Location: USA
Posts: 38
Received 0 Upvotes on 0 Posts
Building a kitchen island. Running electrical conduit.

Hello. I am making a kitchen island and preparing electrical conduit before I lay down new flooring. I cut a groove for the conduit in slab already for the conduit.
The 90 degree PVC elbow has a big radius and its impossible to make it touching the cabinets back wall. It would have to stick out inside the cabinets.

I know that the electrical wire cannot be bent much but we were allowed to use short 90 degree elbows like the one attached below, I was not able to find them anywhere in US.



This is how it looks and how I am planning to do it, but I would want to make it as close as possible to the back cabinet wall.

Pictures link

What is the best and proper way of doing this?
 
  #2  
Old 06-28-19, 02:54 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
Not supposed to use a close elbow as makes it too hard to pull wire through.

Not sure what you are trying to do. Can you cut a deeper channel in the concrete? Otherwise strategic placement of the cabinets with cutting a small notch. The curve is below the bottom shelf so isn't seen.
 
  #3  
Old 06-28-19, 03:00 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
You cannot use that 90. It is not for electrical installation. You need to make a deeper trench.

I would Install a 4x4x1 1/2" metal box in the bottom of the cabinet and run cables or convert the PVC conduit to a flexible conduit (FMC, NFMC, Etc). Just make sure not to exceed 360 degrees of bends between pull points.
 
  #4  
Old 06-29-19, 07:54 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
You cannot use that 90. It is not for electrical installation. You need to make a deeper trench.

Agree! You cannot use a plumbing elbow with conduit.
 
  #5  
Old 06-29-19, 08:02 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Use a shallow angle to bring the 90 up close.to the cabinet instead of at a 90 to the cabinet.
 
  #6  
Old 06-29-19, 08:10 AM
2
Member
Join Date: Jan 2014
Location: USA near Boston, MA
Posts: 2,260
Received 388 Upvotes on 337 Posts
You could use a conduit body: https://www.homedepot.com/b/Electric...z0usncZ1z10wqp

A Type LB on end with the back opening attached to the conduit in the groove and the end opening up into the cabinet.

A Type LL or LR in the groove (cover on top) with a conduit ell on the side opening against the cabinet would also work.

In either case the cover does not have to be accessible after the wires are installed as long as there are no splices or connections inside the fitting.
 
  #7  
Old 06-29-19, 08:24 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,038
Received 515 Upvotes on 420 Posts
In either case the cover does not have to be accessible after the wires are installed as long as there are no splices or connections inside the fitting.
Not true. It does have to remain accessible.
 
CasualJoe voted this post useful.
  #8  
Old 06-29-19, 08:53 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
Joed is correct. Conduit bodies are required to be installed following the same rules as junction boxes, splices or not.
 
  #9  
Old 06-29-19, 08:54 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Hi, what size conduit are you running ? This should do what you are trying to do.
https://www.hardwarestore.com/carlon...hoCBe8QAvD_BwE
Geo
 
 