30amp Dryer Outlet (Single Pole Breaker)

My 200amp panel is pretty full so I started mapping all the circuits since I suspected that there are abandoned circuits or circuits with very small loads on them. I am used to finding dryers on 30amp double pole breakers but it looks like mine is on a 30amp single pole breaker which doesnt make sense to me since it needs 240v.

Attaching a photo of the breaker & panel. The dryer is setup on the one marked (4). Just for reference, I didnt find anything on (2) and my cooktop is setup on 6 & 8 (2x 30 amp single breakers; it turns off if either is flipped)

I just bought the house a few months back and am looking to free up some space for a finished basement. A few circuits are setup to control 1 or 2 outlets or <4 lights.

I checked the dryer outlet and it does have 2 120v legs which seem ok and the unit works great.

Let me know what you think.
 
Attached Images  
Sponsored Links
  #2  
Old 07-06-19, 11:23 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,638
Received 83 Votes on 73 Posts
The dryer is setup on the one marked (4). Just for reference, I didnt find anything on (2)

Hard to tell from the picture, but I suspect that both breakers at (2) and (4) are 30 amp single pole breakers and powering your dryer. If I am correct, you need to replace them with a 2 pole 30 amp breaker.


my cooktop is setup on 6 & 8 (2x 30 amp single breakers; it turns off if either is flipped)

The same applies to (6) and (8), replace them with a 2 pole 30 amp breaker.


Is that a Crouse-Hinds panel?
 
  #3  
Old 07-06-19, 01:25 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,524
Received 236 Votes on 207 Posts
If you are relying on the light or the motor to tell you the dryer is off that is your problem. Both of those devices run off 120 volts so if you turn off the breaker on the leg they are on it will appear the dryer is off.
Try measuring the voltage to ground or neutral from both pins when the one breaker is off.
 
  #4  
Old 07-06-19, 07:48 PM
B
Member
Thread Starter
Join Date: Jan 2014
Location: United States
Posts: 10
Received 0 Votes on 0 Posts
Thanks for the tip and you were right.
One quick follow-up, when I turned off 2 and checked both legs against ground, the side that was turned off was giving 30 volts to ground; why is that instead of 0.
The other side was 120 and I didnt test it when I turned that side off.
 
  #5  
Old 07-06-19, 07:51 PM
B
Member
Thread Starter
Join Date: Jan 2014
Location: United States
Posts: 10
Received 0 Votes on 0 Posts
100% right! Is there any reason someone would set them up this way other than the single breakers were there already? Maybe they have 2 12 guage wires in the area and that made it easier vs running a new thicker wire and using a double breaker?
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: