Grounding rod question
Old 07-09-19, 09:33 AM
P
Hi,
I'm selling my house and the buyers' home inspector is saying the grounding rod on the exterior of my house is not connected (looks like it was cut at some point). Not a tracer wire.
Is the rod necessary and if so what should the green wire be connected to?
Old 07-09-19, 09:42 AM
P
Also I spoke to my gas company and they say no ground wire should be connected to the meter.
Old 07-09-19, 09:52 AM
CasualJoe's Avatar
Received 83 Votes on 73 Posts
I am sure you do not have a ufer ground so yes, you need a ground rod with a minimum of 8 feet earth contact for the Grounding Electrode Conductor to attach to. The minimum size approved ground rod is 1/2" X 8 feet.
Old 07-09-19, 10:35 AM
Received 236 Votes on 207 Posts
That may not even be the ground rod for your electrical service. It may have been placed there by the cable guy. You need to check your main electrical panel and follow the ground wire from there.
If that is for your service then it needs to go into the ground another 4 feet.
Old 07-09-19, 10:45 AM
P
Thanks guys. It is totally possible the cable or FIOS guy put that there a while ago and then snipped it when I switched from one to the other.
I'll investigate the panel to see where the ground goes. I do know that the water main that comes into my house from the street (about 10 ft from the panel) has a ground wire attached to it. But I can't see where it comes from since my basement is finished.
If that is what is happening, is it acceptable to ground the panel to the water main?
Old 07-09-19, 01:40 PM
pcboss's Avatar
Received 83 Votes on 71 Posts
The ground to the water line, if in contact with the soil for at least ten feet and metallic, is the primary ground. A ground rod would be supplemental.
If that rod was placed by a cable tech it was no where near correct.
Old 07-09-19, 01:44 PM
If you have a ground bond to the metal water line then I would just pull that rod and call it good. Water line connection is all you need.
Old 07-10-19, 05:24 AM
I
Received 43 Votes on 41 Posts
FIOS guy
They probably snipped off the old phone ground when they unhooked the copper service and replaced it with the fiber which does not require grounding. Most phone companies that install fiber to the home physically remove the copper wiring making it a permanent switch to fiber.
Old 07-14-19, 07:57 AM
CasualJoe's Avatar
That might be in Canada, but the NEC requires a ground rod in addition to the water line ground.