Transitioning from THWN to NM

Reply

  #1  
Old 07-11-19, 10:09 AM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 378
Upvotes: 0
Received 0 Votes on 0 Posts
Transitioning from THWN to NM

Wiring a sub panel. Running THWN #2 awg wire in 2" conduit. Then will splice to 2-3 NM and make the run to the main panel. From what I've read code says the length of the junction box has to be 8 x the largest raceway. Since I'm using 2" conduit that means my junction box has to be 16" long.

Can I use this box for a junction box?

https://www.zoro.com/wiegmann-straig...nk/i/G0504813/

Of course I have to add end caps.

TIA
 
Sponsored Links
  #2  
Old 07-11-19, 10:49 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,922
Upvotes: 0
Received 37 Votes on 35 Posts
Yes, you can use a wireway or gutter like the type you posted.
 
  #3  
Old 07-11-19, 02:31 PM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 378
Upvotes: 0
Received 0 Votes on 0 Posts
Thank you ibpooks

(extra characters to meet 25 character minimum)
 
  #4  
Old 07-11-19, 03:29 PM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,132
Upvotes: 0
Received 19 Votes on 16 Posts
For splicing NEC specifies 6 times, not 8, so 2" conduit needs 12" box.

See NEC 314.28(A)(2)
 
  #5  
Old 07-11-19, 05:07 PM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 378
Upvotes: 0
Received 0 Votes on 0 Posts
Oh, good, even better. Thanks pattenp
 
  #6  
Old 07-11-19, 05:58 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,812
Received 33 Votes on 29 Posts
For splicing NEC specifies 6 times, not 8, so 2" conduit needs 12" box.

See NEC 314.28(A)(2)
If it is a straight pull it is 8x the largest pipe plus the sum of the other pipes. U or angle pulls it is 6x the largest pipe plus the sum of the other pipes.
 
  #7  
Old 07-11-19, 07:46 PM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,132
Upvotes: 0
Received 19 Votes on 16 Posts
I believe the sum of the other raceways is only of those entering the same wall or row of the box. If it's one in and one out on a different wall it's just the 6 times the largest conduit entering the box.
 
  #8  
Old 07-12-19, 04:54 AM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 378
Upvotes: 0
Received 0 Votes on 0 Posts
I wish they would use zEnglish when they write NEC . It sure would reduce confusion.
 
  #9  
Old 07-12-19, 03:10 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,812
Received 33 Votes on 29 Posts
If it's one in and one out on a different wall it's just the 6 times the largest conduit entering the box
If it is one in and one out on opposite walls (straight pull) it is 8x the largest conduit. Yes, the sum is if there are more then one conduit on a side of a box.
 
  #10  
Old 07-12-19, 09:13 PM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,132
Upvotes: 0
Received 19 Votes on 16 Posts
He said he was doing a splice, not a straight pull, so it's 6 times.
 
  #11  
Old 07-13-19, 05:13 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,812
Received 33 Votes on 29 Posts
Yes. I'm only stating the complete requirements..
 
  #12  
Old 07-15-19, 04:19 AM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 378
Upvotes: 0
Received 0 Votes on 0 Posts
Thanks for the help.

TimH
 