I am curious to how I change out my kitchen breakers to a GFCI Breaker. I have one of these types of breakers. How do I change these out and wire them correctly?
Popular Reply
07-15-19, 05:03 PM
CasualJoe's Avatar
CasualJoe
CasualJoe is offline
Received 21 Votes on 16 Posts
Looks to me like this would be a great application for GFCI receptacles rather than GFCI breakers.
Old 07-11-19, 12:41 PM
Received 42 Votes on 40 Posts
First we'll have to determine if the kitchen is wired as two separate 20A circuits or a single 20A multiwire branch circuit.
You'll need to move the two hots on the outside poles of the kitchen/range quad breaker to either two new GFCI single pole breakers or to a new GFCI double-pole breaker if it's a MWBC.
The new breakers will go into two of the empty slots. Pull off the panel cover and show a picture of the wiring at the quad kitchen/range breaker.
Alarmguy2203 voted this post useful.
Old 07-15-19, 03:35 PM
Sorry if it took so long but here is a picture with the panel cover off.
Old 07-15-19, 05:03 PM
CasualJoe's Avatar
Astuff, Zorfdt voted this post useful.
Old 07-18-19, 10:16 AM
Why is that so? Just curious?
Old 07-18-19, 07:51 PM
pcboss's Avatar
Received 24 Votes on 20 Posts
If you switch to GFI receptacles there would be no need to move breakers in the panel.