Issue with 240 voltage
#1
Member
Thread Starter
Join Date: Jul 2019
Posts: 4
Received 0 Votes
on
0 Posts
Issue with 240 voltage
I have a 240v outlet that was put in professionally a few months ago for my Tesla. On a few occasions, charging has failed and I can't determine the problem. I measured the voltages of the two legs to the 240v outlet. One was 131v and the other was 105v. Is this a problem, or does it not matter as long as it adds up to roughly 240v? I'm thinking this may be the issue that's causing my charging to fail.
#2
It can be an issue if the charging system is a 4 wire (hot, hot, neutral, ground) or if the charging system uses the ground for power.
If it is a 4 wire, that kind of imbalance can be caused by a loose neutral. I suggest going around the house and check your other 240 volt receptacles (Oven, range, dryer, etc) and see if the issue is there as well. You may have a loose neutral at your electricial service.
If it is a 4 wire, that kind of imbalance can be caused by a loose neutral. I suggest going around the house and check your other 240 volt receptacles (Oven, range, dryer, etc) and see if the issue is there as well. You may have a loose neutral at your electricial service.
#3
Those voltages indicate you have a failed neutral connection.
Do the same measurement at another 240 volt device like dryer or stove. This is potentially damaging to any electronics (TV, DVD, etc) in your house. Call the POCO first thing in the AM.
Do the same measurement at another 240 volt device like dryer or stove. This is potentially damaging to any electronics (TV, DVD, etc) in your house. Call the POCO first thing in the AM.
#4
Member
Thread Starter
Join Date: Jul 2019
Posts: 4
Received 0 Votes
on
0 Posts
I just remeasured the voltage and this time it was more nearly balanced. Would running 120v appliances like a dishwasher or microwave cause the voltage to drop to 105v or is the problem something else?
#5
With a bad neutral, voltate at 120 volt receptacles will keep changing with varying usage.
You should unplug all electronics including microwave ovens and also washing machines with digital controls.
Simple test, plug in a hair dryer at a double receptacle. Measure voltage at the other receptacle. Turn on the hair dryer. Measure voltage at the other receptacle again.
Also, if you see incandescent lights unusually and abnormally bright and bluish then you have a neutral problem.
You should unplug all electronics including microwave ovens and also washing machines with digital controls.
Simple test, plug in a hair dryer at a double receptacle. Measure voltage at the other receptacle. Turn on the hair dryer. Measure voltage at the other receptacle again.
Also, if you see incandescent lights unusually and abnormally bright and bluish then you have a neutral problem.
#7
No easy way to test where the problem is unless can see a damaged connection by looking outside. I would just call them. They will tell you if the is theirs. If not then you can call an electrician.
#8
I agree that you should have the power company come out and inspect their side of the service. They will usually do this for free. When you call tell them you measured unequal voltages and they will know what that means.
#10
For those eavesdropping:
Measure voltage at several 120 volt receptacles in different rooms during a time you are experiencing the problem..
If you measure some with too high voltage, some with too low voltage and some with nearly 120 volts then the problem is yours.
If all receptacles are either somewhat too high or somewhat too low then the problem is in your panel or in the service entrance or in the power company equipment.
Measure voltage at several 120 volt receptacles in different rooms during a time you are experiencing the problem..
If you measure some with too high voltage, some with too low voltage and some with nearly 120 volts then the problem is yours.
If all receptacles are either somewhat too high or somewhat too low then the problem is in your panel or in the service entrance or in the power company equipment.
#11
The power company came out and found a loose neutral wire on the pole.
Had that neutral gotten worse.... you could have lost a lot of sensitive equipment in your home.
I'm actually surprised that your neutral problem affected the Tesla charger as they are straight 240v and don't require a neutral.