Questions on 3 way wire

OK, so my cottage had a flood this spring and I will need to replace some NMD wire that got fully submerged for a while. The NMD wire was inside the crawlspace to a junction box where it connected to some outside wire going to two sheds.

The person who wired it up used 3 way wire. In the breaker box I had the white going to the neutral bar, the ground going to the ground bar and the red to one 15 amp breaker and the black to another 15 breaker, just below it.

My question is this. I understand that both the black and the red are hot wires, each capable of carrying 15A, allowing for two separate circuits. Now if I was to run 15A on both circuits at the same time, would the white not be now carrying 30 A, when 3 way wire is used, well above its capacity rating?

Lastly, the breakers in the box were simply two seperate 15A breakers. Is there a device that I can put on these so that a person is forced to turn both off for servicing as opposed to just one. I suspect they should already be like that but they are not. I don't want to have to buy a separate breaker.

Thanks for your help.
 
Sponsored Links
  #2  
Old 08-15-19, 08:44 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,668
Received 74 Votes on 68 Posts
You have what is called a multi wire branch circuit. It is very important that the two hot wire be on separate legs of the service. There should 240 volts between. The neutral will only carry the difference between the hots not the sum since the current on one hot (for lack of better term) cancels the equivalent current on the other hot. If both hots are on the same leg of the panel then the currents will add up.

This a perfect acceptable setup.
 
  #3  
Old 08-15-19, 08:53 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,978
Received 21 Votes on 16 Posts
Is there a device that I can put on these so that a person is forced to turn both off for servicing as opposed to just one.

Yes, it's called a handle tie. Every manufacturer makes them for their particular brand of breaker.
 
  #4  
Old 08-15-19, 09:30 AM
Member
Thread Starter
Join Date: Dec 2006
Location: Canada
Posts: 633
Received 0 Votes on 0 Posts
Thanks guys. That helps.
 
  #5  
Old 08-15-19, 11:53 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,668
Received 74 Votes on 68 Posts
Normally a double pole breaker is used. However a interlock device as provided by the manufacturer can be used. You can't just stick a nail through the holes in the handle.
 
  #6  
Old 08-15-19, 05:42 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,589
Received 337 Votes on 315 Posts
You can't just stick a nail through the holes in the handle.
Why not ? It was perfectly acceptable when I started forty years ago.
 
  #7  
Old 08-15-19, 05:57 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,668
Received 74 Votes on 68 Posts
Why not?
Because code in Canada says.
14-302

(b) in branch circuits derived from a 3-wire grounded neutral system, two single-pole manually operable circuit breakers shall be permitted to be used instead of a 2-pole circuit breaker, provided that
(i) their handles are interlocked with a device as provided by the manufacturer so that all ungrounded conductors will be opened by the manual operation of any handle; and
 
  #8  
Old 08-15-19, 06:29 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,589
Received 337 Votes on 315 Posts
joed...... I'm just joking with you.
 
  #9  
Old 08-15-19, 07:06 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,668
Received 74 Votes on 68 Posts
I saw the grin face after I posted but figure it is a good reference for anyone reading this.
 
  #10  
Old 08-16-19, 06:18 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,978
Received 21 Votes on 16 Posts
Why not ? It was perfectly acceptable when I started forty years ago.

I suppose you could still use this method if you use a UL Listed nail.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: