this is for a 240v air handler 10kW and a 3A motor. Works out to about 45 Amps. Wondering if a 50A breaker will hold reliably. TIA. Cable is nm awg 6.
Old 08-17-19, 09:33 AM
pcboss's Avatar
Received 103 Votes on 89 Posts
You just need to follow the circuit requirements on the data plate of the unit. The proper sizes are already calculated for the unit.
Old 08-17-19, 02:47 PM
Received 1,322 Votes on 1,222 Posts
Very doubtful it will hold. You are talking about a continuous resistive heating load. If it does hold it will be hot. #6 cable is rated for 55A maximum.
What is the size of the disconnect breaker inside the air handler ?
Old 08-17-19, 03:16 PM
T
There is a placard with a max overcurrent of 60 amp, no local disconnect. Although the load center is in site. No 55A breaker avail, but i think a 60 is therefore allowed. I have an extra 50, thus my question.
Old 08-17-19, 03:23 PM
Nearest size to the required so yes..... 60A is allowed.
Old 08-19-19, 05:19 PM
CasualJoe's Avatar
Received 97 Votes on 87 Posts
Sounds like a basic 10 KW electric furnace. Manufacturers have recommended a 60 amp circuit on these practically forever and many manufacturers actually install a 60 amp breaker in the unit as a disconnect. Many years in the past, I wired many 10 KW, 15 KW, 20 KW, quite a few 25 KW and a couple 7.5 KW furnaces.
Old 08-19-19, 05:50 PM
T
I will use the 60A. One interesting note, the Leviton breakers are hydraulic/magnetic, not the common thermal/magnetic. They claim much more consistent trip levels.
Old 08-19-19, 05:57 PM
Hydraulic ? Curious to see how well that works out.