Wall Socket & Lightning Surge?

Hello Everyone. MY friend had a bad lightning storm which blew out the transformer in his back driveway. the Surge went thru and burnt out his washing machine. General Electric repair fixed the washer but could not use the socket it was plugged into. so an electrician put a new outlet in the wall, the washer would still not work in that socket but it works any where else. but when he plugged in a vacuum cleaner to the same new outlet, it worked just fine.. My question is, how come the washer no longer worked in that new outlet but the vacuum cleaner did? Thanks
 
Sponsored Links
  #2  
Old 08-19-19, 11:18 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,227
Received 479 Votes on 449 Posts
how come the washer no longer worked in that new outlet but the vacuum cleaner did?
The only way to answer that question is to check with a voltmeter from hot to neutral and hot to ground. There may be a ground issue bothering the washer.
 
  #3  
Old 08-19-19, 11:21 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
I don't know, but it sounds like a weird problem. Lightning can do some pretty crazy stuff, so it's hard to speculate without seeing it in person. Are there other receptacles on this circuit and do they work normally? Is there anything special about this circuit -- does it have GFCI or AFCI protection?

I suppose I would start by measuring voltages at the troubled receptacle under load. For example, plug in the vacuum and turn it on, then measure the voltages at the other open receptacle.
 
  #4  
Old 08-19-19, 11:34 AM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,439
Received 15 Votes on 15 Posts
My first test would be L1 to N and L2 to N voltage check. Lightning currents are stressful to the system, including the neutral wires.
Its a reach, but the laundry recept may be on a different phase than the other recepts tried.

Vacuum motors have a high tolerance for voltage range.
 
  #5  
Old 08-19-19, 12:01 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,036
Received 113 Votes on 103 Posts
The socket works. The washer works. The problem has to be the plug into the socket. There must a connection issue of some sort.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: