wire size for 200a main breaker

I am installing a 17kw generator with a 200a inservice ats . my existing breaker box is a 200a service so i am removing the main 200a breaker then running wires over to the ats 200a breaker. The distance is 10 feet with the routing of the wire.
My question is what size wire can I use? Some say 3/0 other say smaller like 1/0, can someone shed some light on this for me.
Thanks
steve1
 
Sponsored Links
  #2  
Old 08-26-19, 04:41 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 3,977
Received 16 Votes on 16 Posts
Hi, seems a bit confusing to me what your plan is , can you sketch it out, at any rate the cable size should remain consistent.
Geo
 
  #3  
Old 08-26-19, 05:15 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
From the generator to the ATS use #4 copper, for the rest of the service components which carry 200A use #2/0 copper.
 