Apartment Complex, Questionable Outlet Wiring...

I recently moved into an apartment complex where I noticed I had a building ground fault on 4 of my 9 outlets. Submitted a ticket, maintenance guy who unfortunately wasn't able to communicate very well with me shows up and after an hour of being frustrated, suddenly popped up from behind a table at an outlet and said it was fixed. I retest with my $7 Home Depot tester, shows up ok. Day goes by, I decided to take the plate off and look myself and this is what I see (see attached image). I'm not very electrically literate but everything I've seen on the internet calls this "looping" or "jumping the ground". Is this wired properly, and if not, what can I do about it? Two more maintenance guys (older and assumedly more knowledgable) just left and told me they were just fine by plugging in a similarly cheap tester into the outlets and not pulling the plate off the "fixed" outlet. I do not take myself for a dummy, and I can match up images from the internet pretty well, am I missing something here? Any helpful advice is appreciated.
 
Attached Images  
Sponsored Links

Popular Reply

 
09-03-19, 06:40 PM
Tolyn Ironhand's Avatar
Tolyn Ironhand
Tolyn Ironhand is offline
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,933
Received 55 Votes on 48 Posts
Side note: I suspect you had an "open ground" on your tester, not a "ground fault". A ground fault is what you have now with the bootleg ground. There will be current leaking to ground in the circuit(s).
 
  #2  
Old 09-03-19, 04:02 PM
Member
Thread Starter
Join Date: Sep 2019
Posts: 4
Received 0 Votes on 0 Posts
Update:
I took the plates off of the other three outlets that were previously showing the ground fault and they seem to be wired correctly, with a separate wire running from the ground terminal and a separate wire running from the neutral, both into a collection of wires and wire nuts. Additionally, I checked other outlets in the apartment that never gave a ground fault to compare, and they are wired as the remaining 3 out of 4 previously faulted outlets are wired. It's just this one outlet that he apparently ran from the middle neutral over and around the ground and then into the wall with the bare wire that is my cause for concern. I have a stereo receiver, three computer monitors, a large desktop computer (custom built), and a variety of other electronics that I was planning on plugging into two of the outlets in the series. I'm sure the ground fault cleared up on all four of the outlets bc of what he did to this one as they are no doubt run in a series. Being that these maintenance guys are telling me its ok to wire it this way and I'm renting, I'm just not real sure what to do, and I'm trapped in a state of perpetual half-unpacked bc of the fact that I can't really block/plug anything into these outlets.

Any help would be appreciated, I can post a better photo if it would help.
 
  #3  
Old 09-03-19, 04:15 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,699
Received 77 Votes on 71 Posts
Very dangerous. Instead finding the broken ground he jumpered to neutral. Even though they are tied in the main panel it is not same as tieing them at the receptacle. If the neutral was ever to go open the metal frame on any device could be come live.

The one receptacle jumper corrected the issue on others since they are probably after this one in the chain. If there is a electrician authority in your area this guy should be reported.
 
ShaStaton voted this post useful.
  #4  
Old 09-03-19, 05:56 PM
Member
Thread Starter
Join Date: Sep 2019
Posts: 4
Received 0 Votes on 0 Posts
Very much appreciated @joed. Been up at the apartment complex office trying to sort it out. Lady I've been working with, leasing agent, is incredulous as she lives on the property as well, now the office is worried about their outlets since the supposed senior techs say this is "normal". I'm not selfish but I realize fully I'm not in a place to save the world (college student) and fight for the wiring to be done properly in all the buildings. I just want my stuff fixed and for the place not to burn down. Heaven forbid they have some kind of health emergency go on bc someone wired this place all bojacked. Neways, I guess I'll update when I hear more, they are supposed to have someone come out to take a look at it tomorrow that is rewiring things on the complex somewhere (over 600 apartments here) that sounds like they have more than a few brain cells to run together. We shall see.
 
  #5  
Old 09-03-19, 06:40 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,933
Received 55 Votes on 48 Posts
Side note: I suspect you had an "open ground" on your tester, not a "ground fault". A ground fault is what you have now with the bootleg ground. There will be current leaking to ground in the circuit(s).
 
CasualJoe, ShaStaton voted this post useful.
  #6  
Old 09-03-19, 07:09 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,919
Received 24 Votes on 20 Posts
The hack has created a shock hazard and possibly worse. This will now place current on any metal parts of the system. This is in no way normal. If it is normal someone needs to be taught a lesson in electrical safety and proper wiring.
 
CasualJoe, ShaStaton voted this post useful.
  #7  
Old 09-03-19, 10:33 PM
Member
Thread Starter
Join Date: Sep 2019
Posts: 4
Received 0 Votes on 0 Posts
@Tolyn Ironhand I see I see, I appreciate that. I'm a total novice and just about everything I know now is off forums like these and common sense, thank you for the correction. I am feeling like I need as much ammo as possible to know my stuff in dealing with these cats at the office and the maintenance team. I won't let them leave so easily next time.
 
  #8  
Old 09-04-19, 04:51 AM
Member
Join Date: Mar 2014
Posts: 442
Received 5 Votes on 5 Posts
And ShaStaton do not take it upon yourself to attempt to fix or remedy this situation either by taking the receptacles out of the boxes and checking the wires, rewiring anything, replacing anything even a receptacle. Since you rent this apartment it can be a large liability on your part if in fact you do attempt to fix this on your own. Don't even hire an electrician to come in an fix this issue. If anything were to happen they could pin you with a large liability suit.

We always advise persons who are renting not to work on the electrical part because of the liability issue involved. At this point I would not even hire an electrician to try and resolve it even if you have it in writing from the landlord. Let them hire an electrician then it is there total liability.

Again, this set up of jumping the neutral to the ground is a boot-leg setup and it very dangerous to the occupants of the units. This is what you have to stress to the management office. They are creating a very large liability issue without even knowing it. You can be called their hero for bringing it to their attention and probably possibly saving a life in the future.

Find some articles on boot leg grounds and print them out and give them to the management office.
 
  #9  
Old 09-04-19, 03:05 PM
Member
Join Date: Nov 2015
Posts: 1,196
Received 16 Votes on 15 Posts
Unfortunately this is a typical of apartment maintenance. I know it first hand because I deal with them pretty much everyday.
I have seen lamp cord in the wall to fix bad wiring. I have seen ground jumped to neutral just like yours. I have seen neutral wire jumped to another outlet with bare wire (not cable) through a mounting hole in junction box. (It was even on a different breaker)

Unless you live in a expensive apartment, it will be very hard to get them to fix it correctly. They will just send another maintenance guy and say it is ok as safe.
You will have to demand a licensed electrician to come and fix.
 
CasualJoe voted this post useful.
  #10  
Old 09-04-19, 05:10 PM
Join Date: Jan 2009
Location: Trumbull, CT, USA
Posts: 410
Received 1 Vote on 1 Post
I agree with lambition I am having a problem with an apartment management company they said they would send a tech but are now giving me the run around.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: