Torque spec for 60A Siemens breaker


  #1  
Old 09-06-19, 07:02 AM
D
Member
Thread Starter
Join Date: Jul 2005
Location: Chicago land
Posts: 702
Received 1 Upvote on 1 Post
Torque spec for 60A Siemens breaker

What is torque spec for Siemens 60A breaker? Or what is common trade spec for breakers?
https://www.homedepot.com/p/Siemens-...Q260/100017724
 
  #2  
Old 09-06-19, 08:02 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
There is a label on the breaker that gives the torque specs. AWG 6-4 would be 45 lb-in and AWG 3-2/0 would be 50 lb-in. All I did was look at the picture of a 60A Siemens breaker on the HD website and enlarge the picture so I could read the label. The specs are for Cu-Al 75C wire
 
  #3  
Old 09-06-19, 08:04 AM
N
Member
Join Date: Jan 2012
Location: Canada
Posts: 2,511
Received 21 Upvotes on 18 Posts
I would imagine they would have the torque specs listed on their website for the specific braker.
General rule of thumb (in school and in the field) was always until tight + 1/4 turn.
Using any sort of torque measuring device in a panel (especially live) is a bad idea. Just saying.
 
 