replacing an old 2 slot receptacle with a GFCI

Thank you in advance to anyone who can help. I am replacing an old style 2 slot receptacle with a GFCI to eliminate the need for a 3 prong adapter. The outlet is ungrounded. My question is, if I place the GFCI in the first box on the circuit can I wire standard 3 prong outlets downstream using the load side of the GFCI or must each outlet that I wish to change have its own GFCI? Thanks again.
 
Sponsored Links
  #2  
Old 09-23-19, 11:36 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,773
Received 84 Votes on 77 Posts
You can use the LOAD side. The downstream receptacles should be labelled 'GFCI protected, no ground". I believe these stickers come with the GFCI.
 
  #3  
Old 09-23-19, 12:11 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,042
Received 26 Votes on 20 Posts
I believe these stickers come with the GFCI.

A few labels come with a GFCI receptacle, but usually not nearly enough. I don't believe there is a company that prints and sells these labels commercially so if you need more labels you'll need to make your own. I have thought for many years that this would be a good item for a company like Gardner Bender or Ideal to add to their product list. Most box stores sell the label makers too.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: