Have 12/2, need 12/3. Can I just run single strand of 12 AWG? For light bulb.

Have 12/2, need 12/3. Can I just run single strand of 12 AWG? For light bulb.

Reply

  #1  
Old 09-25-19, 04:14 PM
Member
Thread Starter
Join Date: Oct 2014
Posts: 236
Received 1 Vote on 1 Post
Have 12/2, need 12/3. Can I just run single strand of 12 AWG? For light bulb.

Have bath exhaust fan where the switch controls both at the same time. Want to split it up, so 1 switch for fan, 1 switch for light. Need 12/3 wire to do that, but I have some single strand 12 AWG... can I just use that to run the light?

 
Sponsored Links
  #2  
Old 09-25-19, 05:19 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,810
Received 87 Votes on 80 Posts
No you can not.
All conductors for a circuit must be in the same cable jacket or conduit if single conductors.

The wire pictured does not even look like AC circuit certified wire(THHN).
 
tiresharkdbb voted this post useful.
  #3  
Old 09-25-19, 07:26 PM
Member
Join Date: Nov 2015
Posts: 1,229
Received 18 Votes on 17 Posts
While you cannot run a single wire, you can just pull additional 12/2 instead of replacing existing cable to 12/3.
However, this may not make a difference unless you already have 12/2. It will be about the same amount of work to pull 12/3 anyway and just abandon existing cable.
 
tiresharkdbb voted this post useful.
  #4  
Old 09-25-19, 09:16 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,810
Received 87 Votes on 80 Posts
An additional 12/2 would not be compliant. The hot and neutral would be in different cables since the fan and light share the neutral at the fan.
 
tiresharkdbb voted this post useful.
  #5  
Old 09-25-19, 09:26 PM
Member
Join Date: Nov 2015
Posts: 1,229
Received 18 Votes on 17 Posts
Most cheap fans I saw had separate neutral wires for the light and fan. It probably is different with high end ones?..
 
  #6  
Old 09-26-19, 06:22 AM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,368
Received 11 Votes on 11 Posts
L and N need to be in the same raceway. In order to cancel their mag fields and not cause inductive heating to nearby magnetic metals (boxes, conduit, etc).
Multiple N are ok, again when paired with its corresponding L.
 
  #7  
Old 09-26-19, 06:47 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,810
Received 87 Votes on 80 Posts
If the fan and light have separate neutrals you are fine. If they share a neutral you you can't do it. Parallel conductors are not permitted below #6 and even then they need to be in the same conduit.
 
  #8  
Old 09-26-19, 04:33 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,967
Received 59 Votes on 52 Posts
Parallel conductors are not permitted below #6
Parallel conductors are required to be #1/0 or larger and can be in separate raceways or cables. 310.15(H)(1) and (3)

Wires smaller than 1/0 can be paralleled but they are required to be able to carry the entire load current. 310.15(H)(1)(b)

You can run 2 - 12/2 cables and parallel the neutrals if need or run separately to each part of the fan/light.
 
tiresharkdbb voted this post useful.
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: