Installing new meter box

Hello, I am installing a new meter box and panel to a barn I recently purchased. There are 4 wires coming to the meter underground from the transformer. 3 4/0 aluminum and 1 2/0 aluminum and all have casings. I am wondering where to connect that 2/0 ground cable in my meter box? Do I need to purchase a separate ground bar to install in the box? If so, where would I attach it? Hopefully the picture helps! Thank you! Ryan

Name:  ser2.jpg
Views: 283
Size:  28.5 KB Name:  ser1.jpg
Views: 447
Size:  31.8 KB
 

Last edited by PJmax; 10-13-19 at 09:49 PM. Reason: reoriented pictures
  #2  
Old 10-13-19, 09:19 PM
S
Member
Join Date: Nov 2018
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
Three 4/0 and one 2/0 sounds like 3-phase 208V 200A....
 
  #3  
Old 10-13-19, 09:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
I agree..... there would be three phase legs and a neutral..... no ground.

You're going to need to check with the power company or check the work order to see what was ordered.
 
  #4  
Old 10-14-19, 04:47 AM
R
Member
Thread Starter
Join Date: Oct 2019
Posts: 15
Received 0 Upvotes on 0 Posts
Thanks guys. I swear the electrician told me to order 3 4/0 and 1 2/0 for the line to the transformer. Maybe he meant I just needed a 2/0 ground from the meter box into the ground? I have 200 feet of cable laid out and ready to go in the ground. Am I able to just unravel the ground line from the 200’ ?
 
  #5  
Old 10-14-19, 02:22 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
Typically the neutral is allowed to be smaller in size where you could just unwrap one of the 4/0's.
However.... the smaller cable is usually the last to be added so that means it would be the first to come off. Having three 4/0 cables is going to require ID'ing the neutral.
 
  #6  
Old 10-14-19, 03:51 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
In my area, the power company is responsible for the wires from the transformer to the meter socket in residential services. However, if there is is a pedestal with a main breaker by the road, then that would be your first overcurrent device and would require two hots, one neutral, one ground.

If there is a ped with a meter, your meter would be redundant.
 

Last edited by Tolyn Ironhand; 10-14-19 at 04:41 PM.
  #7  
Old 10-14-19, 03:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
None of the areas I service have a breaker at the pad. That would require too much common sense. Every time I work on an underground service.... I pay the power company for an underground disconnect at the transformer. One time they opened a splice in a buried vault.
 
  #8  
Old 10-14-19, 04:43 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
I should have also mentioned that the above post should have read "in residential services" I have edited the above post.

Commercial services are different. They will mostly have a tap box that the electrical contractor will feed the building from.
 
  #9  
Old 10-14-19, 06:03 PM
R
Member
Thread Starter
Join Date: Oct 2019
Posts: 15
Received 0 Upvotes on 0 Posts
I’m in central Florida. I asked the power company on three different occasions if they install the service line to my barn. They said they will not do that. The power company did tell me if I run 4 cables to their box they will connect all of them for me. So now I’ll thinking I will just unravel 10’ or so of the ground and run in into the main part of my meter box. If I do this would I need a ground rod at my barn? Or will the power company ground suffice?
Thanks for all your comments!
 
  #10  
Old 10-14-19, 06:13 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
If there is no other fuse or circuit breaker between their connection and the meter, then I would say you only need to run three wires. (Hot, Hot, Neutral) You will need at least two grounds at the barn. Normally this is a water pipe, or rebar, and a driven ground rod (or two). The panel in the picture will have the neutral bus bonded to the steel box via a green screw or strap. And to your first question: The neutral will connect to the bus bar on the far right.

Other notes:
I hope you made sure that panel is approved by your power company. My power companies require a meter socket with a bypass handle. Also, I do not see a main breaker on the panel. If it doesn't have one, you can not have more than six circuit breakers.
 
  #11  
Old 10-15-19, 10:21 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
The power company did tell me if I run 4 cables to their box they will connect all of them for me.

I think I'd double check with the power company again to be sure what they are providing is single phase service. It really does sound like a 3-phase 4-wire 120/208 volt system.
 
 