Wiring sub panel questions
#1
Wiring sub panel questions
The house we moved into for some reason on the barn which is just a little cattle barn they had separate power coming in from the road with its own meter. I have a box on the outside of the house with 100 amp main that just feeds the outlets in the basement and the furnace. There's a 60 amp 220 breaker and there that is not being used I talked to an electrician friend of mine and he said I could use that breaker to run power to my barn and just hook it into the main breaker in that panel. I know I have to remove the bonding screw in the subpanel in the barn, do I need to put a separate ground bar on it? And he said to use 4 gauge wire but the closest I can find locally is 2 gauge that's put together in a bundle 3 2 gauge wires and 4 bare for ground. it's aluminum wire is there anything special I need to do since it's aluminum I read you're supposed to put some kind of coating on it whatever you strip off. all I'm going to run in the barn is lights and a couple outlets for battery chargers.
#2
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,657
Received 247 Upvotes
on
211 Posts
Check the type of wire. If it's URD direct bury it is not to enter the structure and has to be terminated on the outside. Which calls for the question if you are direct burying the cable or using conduit underground? Mobile Home Feeder (MHF) is commonly used and is direct bury approved and is allowed to enter the structure because of having the proper insulation requirements to be inside. If using conduit it is best to use either THWN or XHHW wire. When using aluminum wire it's advised to use antioxidant paste on the bare wire ends at the connections. #2 Al is good for up to 90 amps, so it sounds like that maybe overkill for your needs.
#4
Member
How many feet is it from where the power would come from the house panel to the barn? There may be voltage drop to consider.
#7
So I need wire that has the bare ground wire insulated? That's what I seem to find online. Lowe's has 3 wire cable twisted together so I'm assuming I would need to run a separate 4th wire.
#9
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,657
Received 247 Upvotes
on
211 Posts
If aluminum, yes the ground needs to be insulated. In SER the ground is bare and the outer jacket does not protect it from water and when underground it will turn to mush. You need wire that is approved for wet locations in conduit underground.
You can use SER above ground and transition via a junction box to individual wires of THWN or XHHW in conduit to go below ground.
You can use SER above ground and transition via a junction box to individual wires of THWN or XHHW in conduit to go below ground.
#11
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,657
Received 247 Upvotes
on
211 Posts
Be careful of what the 3 wire is. Most of the twisted 3 wire cable is URD for power distribution and is not fire rated to enter the structure. So if you are planning to have this wire run into the structure it needs to be approved for interior use. And you do need the feeder to be 4 wires, 2 hots, 1 neutral, one ground. Check the 3 wire insulation rating that it's just not USE-2, but also carries the RHH/RHW ratings for interior use.
#12
I found the wire at another local supplier. Thank you for pointing me in the right direction. Is there anything else I need to know for hooking up the sub panel. I know I have to remove the bonding screw in the subpanel.