electrical drops from ceiling that meet fire code


  #1  
Old 11-15-19, 09:29 AM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
electrical drops from ceiling that meet fire code

Hi ya'll,

I have a commercial application here where we have electrical cords that are hanging from the ceiling that have a power strip on the end. According to the fire marshal this doesn't meet code and we need an electrical drop. Anybody here know what that is even. My guess is this electrical drop would have to somehow connect on the outlet box on the ceiling and have flexible conduit running from it with a receptacle on the end. Have never seen anything like that before though. So am not sure what he wants me to do.

Thanks,
-Mike
 
  #2  
Old 11-15-19, 09:35 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
I have a commercial application here where we have electrical cords that are hanging from the ceiling that have a power strip on the end. According to the fire marshal this doesn't meet code and we need an electrical drop.

First thing I would ask the Fire Marshal is what code does this not meet, the NEC or the local fire codes? And then, what specific section and paragraph of that code. Cord drops are perfectly acceptable to machines or benches in a commercial/industrial setting, but they must be installed correctly.
 
  #3  
Old 11-15-19, 09:51 AM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
So how about using this for the conduit:


This to connect the conduit to the outlet boxes:


And finally this as the end electrical box:




The end electrical box will not be secured to anything but will just be dangling there. Not sure what is best to use for that.
 
  #4  
Old 11-15-19, 09:57 AM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
according to the report 2015 IFC 605.5 was the concern... Is what I am considering correct? Any better way? Thanks
 
  #5  
Old 11-15-19, 01:15 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,977
Received 194 Upvotes on 170 Posts
You probably need strain relief at both ends of the cord. You would also need to meet the conditions that allow flexible cord usage.
 
  #6  
Old 11-15-19, 01:22 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,036
Received 515 Upvotes on 420 Posts
It appears he believes these to be extension cords.

https://www.campusfiresafety.org/Por...-25-000000-000

605.5 Extension cords. Extension cords and flexible cords shall not be a substitute for permanent wiring. Extension cords and flexible cords shall not be affixed to structures,extended through walls, ceilings or floors, or under doors or floor coverings, nor shall such cords be subject to environmental damage or physical impact. Extension cords shall be used only with portable appliances.
 
  #7  
Old 11-16-19, 04:53 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,073
Received 161 Upvotes on 147 Posts
Ceiling type

What type of ceiling do you have? cords can’t be used above them, post some pics of what you have, you could install a junction box on the ceiling and then drop the cord down from that using strain relief connectors on both ends and a Sky tie to support the cord at the top.
https://www.galco.com/buy/Adalet/SH-50
Geo
 
  #8  
Old 11-16-19, 12:58 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
I have installed hundreds of cord drops for machines, equipment, or for general purpose use using SO or SJO cord and boxes and receptacles on the end.

The cord must be properly supported, and may not pass through a wall or ceiling. If portability is required you could install a twist lock receptacle at the ceiling but otherwise hardwiring them is the best option.
 
  #9  
Old 11-18-19, 11:23 AM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
SO if I was to use the SJO cord I assume I use this at one electrical box to secure the SJO cord:




And then on the end I install something like this:



This is what it looks right now:
 
  #10  
Old 11-18-19, 12:45 PM
T
Member
Join Date: Oct 2005
Location: USA
Posts: 1,569
Received 74 Upvotes on 69 Posts
My factory here has on the order of a hundred SO drops. The key is NOT to have a male plug on the end; too much like an extension cord that is in "permanent use".
 
  #11  
Old 11-18-19, 01:41 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,036
Received 515 Upvotes on 420 Posts
I would say you for sure would need some sort of cable restraint on those cords. They can't just hang by the plugs.
 
CasualJoe voted this post useful.
  #12  
Old 11-18-19, 03:05 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,073
Received 161 Upvotes on 147 Posts
  #13  
Old 11-18-19, 05:56 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
Use a 1900 box (4"x4") cover with a KO in it and attach a strain relief connector like Geo posted. With most SO cord you will need a 3/4" and 1/2" for SJO cord.
 
  #14  
Old 11-20-19, 10:19 AM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok so the installation would look like this.

On the electrical box on the ceiling I knockout one of the holes and then install what Geo posted in the knockout:
https://www.elecdirect.com/cable-mes...43-cable-range

I install the 1/2" SJO cord in the knockout with the strain relief connector and make the electrical connections in that electrical box on the ceiling.

Finally on the end I install a 1900 box with one of the knockouts out. I will then install probably two receptacles in the 1900 box and put on a metal cover. This 1900 box will be located on the ground; so this is how I extended the electrical supply from the ceiling to the ground.

A final question is do you think it is a good idea to use a twist lock electrical connection on the ceiling for strain relief? This has the benefit of increased portability as mentioned.
 
  #15  
Old 11-20-19, 06:56 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,977
Received 194 Upvotes on 170 Posts
I believe the bottom box must have a threaded hub. A stamped 1900 box is not listed for the use described and the knockout could be pushed in and create a shock hazard.
 
  #16  
Old 11-21-19, 04:44 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,073
Received 161 Upvotes on 147 Posts
Hi, the ceiling box would have a splice, no need for plug, also cord should have a strain relief connector on both ends.
Is this on a suspended ceiling?
Geo
 
  #17  
Old 11-21-19, 11:29 AM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
Nope, it isn't a suspended ceiling... Yeah I was going to do the splice on the ceiling box granted that it is smarter to hard wire it in versus using a twist lock up there.

Hello pcboss, what kind of threaded box were you considering?
 
  #18  
Old 11-21-19, 04:19 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,073
Received 161 Upvotes on 147 Posts
Hi, we have always used 4” Sq and never had an issue with knock outs being pushed in, although I suppose it could happen.
Geo
 
 