Standard height of the ground to hang a control panel?

Reply

  #1  
Old 11-19-19, 10:18 AM
Member
Thread Starter
Join Date: Oct 2014
Posts: 643
Received 0 Votes on 0 Posts
Standard height of the ground to hang a control panel?

I have a panel which features various indicator lights and switches on the outer door, is there a standard height off the ground to put it?
 
Sponsored Links
  #2  
Old 11-19-19, 10:24 AM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,398
Received 12 Votes on 12 Posts
What country? and is this this industrial?
79" max from deck to the highest user operating device is a popular spec.
 
  #3  
Old 11-19-19, 10:43 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,884
Received 96 Votes on 88 Posts
Not sure about control panel but breaker panels in Canada.

Panelboards in dwelling units shall be installed as high as possible, with no overcurrent device operating handle positioned more than 1.7 m above the finished floor level.
 