Siemens quad legs
Siemens quad legs
On a Siemens quad, eg a 15-20/20-15,
are the top and bottom (outside) breakers always on different legs?
Thanks. On another note, if I put a single pole 15A it seems to fill up the A and B slot at the same time.
i thought it could only be one leg?
The Siemens quad breaker is 4 half size breakers attached together to use a standard two breaker space.
If you use a half size breaker...... you can put two on the same leg.
A standard size breaker takes up one slot on only one leg.
The standard size takes up one slot but it's across A and B on the labels. Seems weird.
same with a double pole standard it goes across ABAB the same space as a quad
I'm not sure what you are seeing but a single pole breaker cannot connect to both legs as that would be creating a dead short.
I get what you're saying it should be
A
A
B
B
But my labeling seems to say
A
B
A
B
Picture....
Panel https://imgur.com/gallery/7GnmdRW
A
A
B
B
A
B
A
B
Picture....
That lettering is just for the ease in labeling 1/2 size breakers.
It has nothing to do which leg on the service it's on.
1A, 1B, 2A, 2B are all on the A leg of the panel.
3A, 3B, 4A, 4B are all on the B leg of the panel.
Etc....
Etc....
Siemens usually uses L1 and L2 instead of A and B to refer to the legs of the power feed (also L3 instead of C for 3 phase).
This eliminates the ambiguity discussed in the last few replies.
Even if (I don't know of any examples) the individual breakers in a double wide quad breaker unit were connected to L1, L2, L1, L2 in order via the usual two fins underneath, it will still work correctly if you connected one 240 volt circuit and handle tie to the two outer terminals and connected a second 240 volt circuit and handle tie to the two middle terminals.