Electrical run partially in conduit


  #1  
Old 12-15-19, 08:07 AM
V
Member
Thread Starter
Join Date: Dec 2019
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Electrical run partially in conduit

Hi,
I am remodeling my basement and I am running a few new circuits up through my attic and down into my basement. Once in the basement I am drilling holes through the floor joists to get to the locations where I need outlets. I then need to go down the poured concrete walls. The wire will then be covered with insofast insulated wall panels so I am pretty sure I need conduit against the walls. It's going to be near to impossible to get conduit into the attic. Is it to code to run the NM 12/2 all the way to the concrete walls and then use conduit to go down to outlets and between outlets? If so do I need a certain box before going into the conduit. Or can the wires just go from exposed right into conduit. Thanks Mike
 
  #2  
Old 12-15-19, 08:29 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,319
Received 874 Upvotes on 737 Posts
Yes, you can sleave nm cable in a raceway. You just gave to follow the conduit fill rules and install it properly. No box is needed at the end of the conduit, just install a bushing or connector on the end of the conduit where the cable enters. For running between boxes with conduit I would recommend using individual THHN conductors as it is easier to install.
If you do use NM cable you do not remove the sheath from the cable when running it in the raceway.
 
  #3  
Old 12-15-19, 08:43 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,036
Received 515 Upvotes on 420 Posts
The wire will then be covered with insofast insulated wall panels so I am pretty sure I need conduit against the walls
There is no requirement to put these wires in conduit.
 
  #4  
Old 12-16-19, 09:43 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
There is no requirement to put these wires in conduit.

But I would. ......................
 
  #5  
Old 12-16-19, 12:04 PM
V
Member
Thread Starter
Join Date: Dec 2019
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok I was on the fence about the conduit. I was under the assumption that putting them against my poured concrete foundation would require conduit even though it 2 inches from nailing surface.
is the extra protection necessary? Are the other benefits to the conduit. Appreciate the input.
 
  #6  
Old 12-16-19, 12:12 PM
T
Member
Join Date: Oct 2005
Location: USA
Posts: 1,569
Received 74 Upvotes on 69 Posts
Its a choice. I would (and do) use EMT for the vertical drop, but not for the sideways runs. It protects against drilling into the wire for hanging pictures and such. OTOH, if it is behind 2" or more of insulation, then that's enough for me.
 
  #7  
Old 12-16-19, 12:18 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,036
Received 515 Upvotes on 420 Posts
It is not required. It is not going to be subject to damage after you cover it with the panels.
 
  #8  
Old 12-17-19, 06:34 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,704
Received 273 Upvotes on 230 Posts
There is no fill rules for sections of conduit when used as a protective sleeve. Conduit just needs to large enough so the pull is easy so not to damage the cable. Be sure to use bushings on open ends of conduit to protect cable from sharp edges.
 
 