Adding a ground wire to 2 conductor wiring.

Reply

  #1  
Old 12-23-19, 06:56 AM
G
Member
Thread Starter
Join Date: Dec 2007
Location: USA
Posts: 238
Received 0 Votes on 0 Posts
Adding a ground wire to 2 conductor wiring.

Some circuits in my house are 2 conductor wire in very good condition.

1) Can I add a grounding wire from the main electrical box the first junction box and then between each junction box.

2) Can I consider this 2 conductor+ ground wire a three-conductor cable and extend it? I have a single lighting fixture that was once knob and tube. It would be nicer looking if it could be added to the circuit with 2 conductor + grounded boxes. The lighting fixture is wired with romex from circuits on the upper floor in a way that is unattractive visually (wiremold conduit).
 
  #2  
Old 12-23-19, 11:02 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,726
Received 297 Votes on 255 Posts
1. yes you can
2. yes you can
 
  #3  
Old 12-24-19, 07:02 AM
G
Member
Thread Starter
Join Date: Dec 2007
Location: USA
Posts: 238
Received 0 Votes on 0 Posts
Thank you for answering my questions.

Are there any rules to the ground wire?

1) Can I attach the ground wire to the outside of the box with a screw?

For example, instead of disconnecting a lighting fixture to work inside the box can I from above the box screw a grounding wire to the box? I will later test each lighting fixture to determine if it is grounded.

2) Can a ground wire be exposed uninsulated wire?

3) Can multiple ground wires be joined outside an electrical box?

Inside a crawlspace can I connect multiple ground wires with a twist nut outside of any junction box?

4) Can a junction box be grounded to more than one circuit?

For example, In an attic crawl space, there are 2 junction boxes on 2 different grounded circuits with 2 separate circuit breakers. Can a ground wire be attached between those 2 junction boxes?
 
  #4  
Old 12-24-19, 07:07 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,726
Received 297 Votes on 255 Posts
1. no. I has to go inside and it has to be a proper ground screw.
2. yes
3. not sure about code on that one.
4. yes. all grounds are always all connected. One ground wire from the panel can service several different circuits. It must be sized to the largest circuit.
A ground wire doesn't have to go back to the panel. It can go to any other point on grounding system that has the same gauge or larger wire.
 
Zorfdt voted this post useful.
  #5  
Old 12-24-19, 07:13 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,803
Received 252 Votes on 220 Posts
3) Can multiple ground wires be joined outside an electrical box?
Any splice is required to be inside a box and the box is required to be accessible. The only exception would be low voltage wiring.
 
  #6  
Old 12-24-19, 08:27 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,513
Received 125 Votes on 99 Posts
I have to ask because I am not clear about what wiring you have. Is it old 2 wire romex without a ground? If so you cannot add a ground wire independent of the cable. If the wiring is individual wires in a metal conduit system you can pull a ground or use the conduit as a ground.
 
  #7  
Old 12-24-19, 08:31 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,803
Received 252 Votes on 220 Posts
Is it old 2 wire romex without a ground? If so you cannot add a ground wire independent of the cable.
That is not correct. See below.



300.3(b)

2) Grounding and Bonding Conductors. Equipment grounding conductors shall be permitted to be installed outside a raceway or cable assembly where in accordance with the provisions of 250.130(C) for certain existing installations or in accordance with 250.134(B), Exception No. 2, for dc circuits. Equipment bonding conductors shall be permitted to be installed on the outside of raceways in accordance with 250.102(E).
 
geo8rge voted this post useful.
  #8  
Old 12-24-19, 12:57 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,513
Received 125 Votes on 99 Posts
It has been ages since having to deal with old wiring. I just had 300(B) only in my head. I had forgotten about the "unless otherwise permitted" in (2). Thanks for the correction.
 
  #9  
Old 12-26-19, 11:12 AM
G
Member
Thread Starter
Join Date: Dec 2007
Location: USA
Posts: 238
Received 0 Votes on 0 Posts
Picture, no question but it looks like the ground is uninsulated copper.

250.130(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions.



https://www.electricallicenserenewal...sectionID=52.0
 
  #10  
Old 12-26-19, 07:10 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,223
Received 103 Votes on 89 Posts
The ground can be bare or insulated.
 
  #11  
Old 12-27-19, 06:08 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,556
Received 157 Votes on 139 Posts
Reminder, if the box is metal, it needs to be grounded, as does the device.