Wire size for electric furnace

I bought a 15kw electric furnace. 240vac 1ph 60hz the manual says supply wire size must be in accordance with NEC codes. What size wire do I need?
 
  #2  
Old 12-31-19, 10:21 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,038
Received 515 Upvotes on 420 Posts
What size breaker does it say to install for the furnace?
15kw at 240 volts is 62.5 amps. You probably need at least 80 breaker. I expect #3 copper or #1 aluminum would be OK if they spec an 80 amp OCD.
 
  #3  
Old 12-31-19, 06:21 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
15 KW electric furnaces typically require two circuits, one a 30 amp circuit with 10-2 NM-B cable and the other a 60 amp circuit with 6-2 NM-B cable. Most new furnaces will have breaker disconnects in them and that is where the circuits terminate, in the lugs of those breakers.
 
  #4  
Old 12-31-19, 08:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
You could post the make and model of that furnace for us.
 
 