I bought a 15kw electric furnace. 240vac 1ph 60hz the manual says supply wire size must be in accordance with NEC codes. What size wire do I need?
#2
Member
What size breaker does it say to install for the furnace?
15kw at 240 volts is 62.5 amps. You probably need at least 80 breaker. I expect #3 copper or #1 aluminum would be OK if they spec an 80 amp OCD.
15kw at 240 volts is 62.5 amps. You probably need at least 80 breaker. I expect #3 copper or #1 aluminum would be OK if they spec an 80 amp OCD.
#3
15 KW electric furnaces typically require two circuits, one a 30 amp circuit with 10-2 NM-B cable and the other a 60 amp circuit with 6-2 NM-B cable. Most new furnaces will have breaker disconnects in them and that is where the circuits terminate, in the lugs of those breakers.