Options for bucking 250 volts to 220.
Old 01-02-20, 01:57 PM
D
I have a cnc lathe that requires 220 volts on a 3 phase 100 amp circuit. The building is providing 250 volts. What are my options? The manufacturer is saying I can run it this way but will be at the max tolerance for the machine and any spike in voltage could cause more sensitive components (like control boards) to fry.
Old 01-02-20, 05:37 PM
Tolyn Ironhand's Avatar
Received 253 Votes on 221 Posts
Nominal voltage for three-phase power is either 120/240v delta or 120/208v wye. The 120/240v delta will be 240 volts between phases and 120 volts between phase A and phase C. Phase B voltage will be 208v to ground/neutral.
Your options are to get a 240 delta to 120/208 wye three-phase transformer or get two 12/24v (or 16/32v) buck/boost transformers to reduce the voltage down closer to 220v. What you need will all depend on the machine you are connecting and if it requires a neutral.
dancar voted this post useful.
Old 01-02-20, 08:40 PM
Received 1,348 Votes on 1,246 Posts
The lathe can't need 100A @ 3phase. That would be massive.
What is the ID plate amp requirement.
Old 01-03-20, 08:13 AM
D
The plate requests 96 amps (called it 100 just to round up since you can't get 96 amp breaker).
Old 01-03-20, 08:19 AM
D
Ironhand, thanks for the reply. Machine does not require a neutral. I have been looking at (2) 12/24 buck/boost transformers. I was hoping for a more economical solution but it appears this is about the only option I have. Do you know if all brands would convert the same? I found model T-1-11686 from Acme ($600 Grainger) will do 250 down to 227 and provide 137amps at that conversion. They also sell a Square D model 3S43F for $1,200. I am not sure why the massive price swing. Any ideas or suggestions? I was looking to stay as close to $400 as possible but am not sure where else to find one of these.
Old 01-03-20, 10:51 AM
CasualJoe's Avatar
Received 97 Votes on 87 Posts
Is that a European or Asian manufactured CNC machine? I don't recall ever seeing a 3-phase motor labelled for 220 volts.
Old 01-04-20, 06:17 AM
I have seen some machines out of Japan requiring 220v.
A buck/boost transformer(s) only needs to carry to the difference of the load you are running. According to the info I am seeing online it appears that you need 2 3kva buck/boost transformers. You should confirm this.
I have not seen any differences between brands of transformers and they all do the same job. Transformers have no moving parts and generally last for 50 years or more. I would not hesitate buying used ones from a local used equipment dealer.
Old 01-04-20, 12:15 PM
You may see aluminum vs copper windings.