Getting a shock from kitchen appliances?

I have an old kitchen (1950's) and appliances. Range top, Espresso machine(SS), built in oven, hood, a metal SS sink. So I noticed by no subtle means that a current is passing thru these appliances when we touch and make contact between two close appliances. I have put a meter between a few of them and I get all kinds of low voltages.Where do I begin in trouble shooting to find the problem. The only thing I can add is maybe ten years ago I removed the top element in the built in wall oven. I thought I capped off the loose wire ends. Its a bit of a pain to pull out the oven, but if I need to start there I will.
PS I also see the outlets are testing open ground
 
Sponsored Links
  #2  
Old 02-15-20, 05:19 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,173
Received 140 Votes on 126 Posts
Start by checking all the ground connections inside the appliances and the electrical system boxes.
 
  #3  
Old 02-15-20, 09:11 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,357
Received 48 Votes on 39 Posts
I also see the outlets are testing open ground
In a 1950s kitchen I would expect to see 2-wire NM cable with no grounding conductor so open ground would be correct because there wouldn't be a ground wire. Use your meter and measure the voltage between the frame of each appliance to the stainless steel sink and see what you get.
 
  #4  
Old 02-16-20, 03:01 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 4,919
Received 53 Votes on 50 Posts
I would also check if your plumbing system is grounded/bonded. Does it have a wire connected to the metal piping from the main panel. Nowadays it needs to be near where it comes into the house - but yours is likely at the closest point between the piping and electrical box.

If there's an accidental short between the plumbing pipes and electrical system - this will ensure that the breaker trips quickly.
 
  #5  
Old 02-16-20, 06:41 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 3,813
Received 44 Votes on 42 Posts
At some point in the troubleshooting you will need to disconnect each appliance from power. At least for the range, you can unplug it although the plug could be hard to reach.

Measure resistance from the appliance frame or exposed metal to each of the "hot" supply wires coming from it (or the plug prongs one at a time. You should get nearly infinite resistance (or no continuity) from either hot prong or wire to the frame. Otherwise there is a defect in the appliance.

Flip off the breaker for the appliance circuit (each appliance circuit in turn) With the power off measure resistance from each hot conductor to the metal sink. You should get nearly infinite resistance for these tests also..
 
  #6  
Old 02-17-20, 04:41 AM
pugsl's Avatar
Forum Topic Moderator
Join Date: Mar 2008
Location: United States
Posts: 8,645
Received 32 Votes on 29 Posts
Has any plastic piping been added to house? if so if may have broken the ground there.
 
  #7  
Old 02-17-20, 05:57 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 3,813
Received 44 Votes on 42 Posts
A grounding electrode conductor (fat wire from panel) to approved water pipe connection can double as the needed bonding jumper from cold water plumbing to the panel neutral (house ground reference; root of the grounding electrode system). To complete this connection another bonding jumper is needed across the meter inlet and outlet..

If there is no pipe grounding electrode, i.e. the main water pipe is plastic exiting the house, then the aforementioned long fat wire is no longer a GEC but can be a bonding jumper. Then, if the former were not present, a bonding jumper (same sized wire) elsewhere, for example from the cold water plumbing at a point closest to the main panel, to the panel, is acceptable.

Grounding electrodes including ground rods are not good and sufficient to prevent electric shock from energized appliance exteriors and other exposed metal that gets energized. Running a ground wire (equipment grounding conductor), even haphazardly, attached to the metal exterior and also to a good ground in the panel with the breaker for the appliance circuit (or to a GEC) will greatly reduce the hazard. (Such a haphazard EGC is often used for reducing hum in stereo systems and other electronics or improving reception of ham radio.)

It is still necessary to troubleshoot and fix the problem causing the electric shock.
The EGC will do one of two things:
1. Reduce the potential difference (voltage) between the far end (the appliance exterior or whatever) and the panel connection (house ground) which will greatly reduce the chance of accidental electrocution.
2. Draw enough power to trip the breaker.
The EGC in performing #1 well can still result in a small continual or continuous current flow that makes a noticeable increase in your electric bill.
 

Last edited by AllanJ; 02-17-20 at 06:24 AM.
  #8  
Old 02-18-20, 01:50 PM
H
Member
Join Date: Nov 2012
Location: USA
Posts: 1,476
Received 59 Votes on 51 Posts
I have an old kitchen (1950's) and appliances.
If it is 1950s wiring, you probably had un-polarized plugs, and one of the polarized plugs has"hot" and "return" swapped.
Try a simple "plug in circuit tester"

with an adapter.

which should tell you what is going on.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: