Need help with panel wiring


  #1  
Old 02-15-20, 01:19 PM
J
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Need help with panel wiring

I have a panel in an shed. The panel is the shed is wired to a 30 amp double pole breaker at the main house panel. They put a 60 amp breaker in the panel in the shed and are using one leg of that breaker to supply 120 V for the lights and outlets.

I want this done properly so can I remove that 60 amp breaker and use 2 15 amp breakers in it's place? Remember the panel is connected to a 30 amp breaker at the main house panel. I have no idea why the used a 60 amp single breaker in the shed panel.

Below is a picture of the shed panel.

Thanks
 
Attached Images  
  #2  
Old 02-15-20, 02:44 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes on 207 Posts
The breaker in the shed needs to be sized to the wire size used for the circuit. If the wire is #14 then you do need to change to a 15A in the shed. But to answer your question directly the dp60 can be replaced with 2 single pole 15A. Also a ground bar needs to be added and the neutral isolated from the ground. Plus ground rods should be added. A clamp is needed on the romex at the box entry. Is the feeder wire to the shed regular romex and is it underground?
 
  #3  
Old 02-15-20, 03:19 PM
J
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
It does have a ground bar in it although very small places for 2 wires. The cable is underground in a PVC pipe going to the main breaker box where it is tied into a 30 amp double pole breaker. The wire is 12 gauge that currently runs 6 outlets and 2 lights.

Just to be clear the box pictured above is what is in the shed.

Could another option be to replace that breaker pictured above with a 20 amp double pole breaker and run 2 circuits one off each pole of the 20 amp double pole?
 
  #4  
Old 02-15-20, 03:45 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes on 207 Posts
The white neutral should be connected to a separate bar from where the bare ground wire is connected. The neutral bar needs to be insulated from the box. If the circuit wire is #12 the protecting breaker can be a 20A, either using a single or double pole. If the feeder from the house is white romex in conduit underground that is not appropriate. The only romex allowed underground is type UF.
 
  #5  
Old 02-15-20, 05:58 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,934
Received 491 Upvotes on 403 Posts
I would use that 60 amp breaker to supply a separate small breaker panel. Install your 15 or 20 amp breakers in there.
 
 