Need help with panel wiring
#1
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Need help with panel wiring
I have a panel in an shed. The panel is the shed is wired to a 30 amp double pole breaker at the main house panel. They put a 60 amp breaker in the panel in the shed and are using one leg of that breaker to supply 120 V for the lights and outlets.
I want this done properly so can I remove that 60 amp breaker and use 2 15 amp breakers in it's place? Remember the panel is connected to a 30 amp breaker at the main house panel. I have no idea why the used a 60 amp single breaker in the shed panel.
Below is a picture of the shed panel.
Thanks
I want this done properly so can I remove that 60 amp breaker and use 2 15 amp breakers in it's place? Remember the panel is connected to a 30 amp breaker at the main house panel. I have no idea why the used a 60 amp single breaker in the shed panel.
Below is a picture of the shed panel.
Thanks
#2
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes
on
207 Posts
The breaker in the shed needs to be sized to the wire size used for the circuit. If the wire is #14 then you do need to change to a 15A in the shed. But to answer your question directly the dp60 can be replaced with 2 single pole 15A. Also a ground bar needs to be added and the neutral isolated from the ground. Plus ground rods should be added. A clamp is needed on the romex at the box entry. Is the feeder wire to the shed regular romex and is it underground?
#3
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It does have a ground bar in it although very small places for 2 wires. The cable is underground in a PVC pipe going to the main breaker box where it is tied into a 30 amp double pole breaker. The wire is 12 gauge that currently runs 6 outlets and 2 lights.
Just to be clear the box pictured above is what is in the shed.
Could another option be to replace that breaker pictured above with a 20 amp double pole breaker and run 2 circuits one off each pole of the 20 amp double pole?
Just to be clear the box pictured above is what is in the shed.
Could another option be to replace that breaker pictured above with a 20 amp double pole breaker and run 2 circuits one off each pole of the 20 amp double pole?
#4
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,634
Received 243 Upvotes
on
207 Posts
The white neutral should be connected to a separate bar from where the bare ground wire is connected. The neutral bar needs to be insulated from the box. If the circuit wire is #12 the protecting breaker can be a 20A, either using a single or double pole. If the feeder from the house is white romex in conduit underground that is not appropriate. The only romex allowed underground is type UF.