Metal Flex Conduit vs EMT Conduit


  #1  
Old 02-21-20, 05:44 AM
G
Gen
Gen is offline
Member
Thread Starter
Join Date: Jun 2006
Location: US
Posts: 701
Received 9 Likes on 8 Posts
Metal Flex Conduit vs EMT Conduit

Seeing electric installations on this can be confusing to me. Can someone give me the basics on when wire should be in regular conduit vs when flex BX type conduit/cable can be used? Should BX conduit be used in an exterior wall?
 
  #2  
Old 02-21-20, 08:10 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,857
Received 216 Likes on 183 Posts
Basically EMT in open accessible areas where installation is easy and you want a clean looking install. FMC on tough areas to place EMT. MC cable where circuit needs to be fished due to lack of accessibility. They all have there own installation requirements under the NEC. Regular MC cable can go in an exterior wall as long as it's not subject to getting wet, otherwise it needs to be jacketed MC or listed for wet areas.
 
  #3  
Old 02-21-20, 08:19 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,600
Received 156 Likes on 142 Posts
Hi, it depends on the installation, What are you trying to accomplish? BX type conduit or (flexible metal conduit ) is for flexibility at motors etc. typically not longer than 6í, metal type can not be used outside, Non metallic flexible conduit must be used.
Geo
 
  #4  
Old 02-21-20, 09:49 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,857
Received 216 Likes on 183 Posts
The 6' rule on Flexible Metal Conduit (FMC) is if the FMC is being used as the ground. If a ground conductor is run in the circuit the 6' doesn't apply.
 
The following users liked this post:
  #5  
Old 02-21-20, 10:44 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,600
Received 156 Likes on 142 Posts

Got it! Thanks for that clarification.
Geo
 
  #6  
Old 02-21-20, 12:09 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,341
Received 462 Likes on 382 Posts
BX is not a conduit. It is a cable.
 
  #7  
Old 02-22-20, 09:57 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 11,173
Received 166 Likes on 149 Posts
Non metallic flexible conduit must be used.

Outside I generally always specified Liquidtight Flexible Conduit and liked the type with the copper bonding strip.
 
  #8  
Old 02-24-20, 04:30 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 15,029
Received 627 Likes on 536 Posts
BX, AC, MC, MC are all cables that come from the manufacturer as an assembly with wires included. FMC aka "Flex" or "Flexible Metal Conduit" is a raceway that is required to be installed and then wires pulled inside it.
 
The following users liked this post:
 