Contactor selection for heater circuit
#1
Member
Thread Starter
Join Date: Feb 2020
Posts: 2
Received 0 Votes
on
0 Posts
Contactor selection for heater circuit
I need help choosing the right contactor for a Yoga room heat project. 3 - 120v 1500w infrared heaters controlled by either 120v smart switch(turn on heaters remotely thru an app) or a 24v wifi t-stat(also ability to set temp remotely).
2 pole 30A contactor?
2 pole 30A contactor?
#2
Welcome to the forums.
A 120v 1500w heater cannot be connected to a circuit over 20A.
You should put each heaters on its own 20A circuit.
You could use a 3 pole contactor to switch all three heaters. A thermostat could control a contactor like this directly. An example of one is below.
Three pole contactor 24vac coil
A 120v 1500w heater cannot be connected to a circuit over 20A.
You should put each heaters on its own 20A circuit.
You could use a 3 pole contactor to switch all three heaters. A thermostat could control a contactor like this directly. An example of one is below.
Three pole contactor 24vac coil
#3
Member
Thread Starter
Join Date: Feb 2020
Posts: 2
Received 0 Votes
on
0 Posts
AHH! Not I totally get it. For some reason I thought I was fusing the contactor at total amp Capacity. It's just a pass thru device to have all heaters turn on at the same time. Thank you for clearing this up for me