Tandem Breaker


  #1  
Old 03-07-20, 10:41 AM
M
Member
Thread Starter
Join Date: Mar 2020
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tandem Breaker

Hello:
My breaker box looks full and I want to install a 30 amp breaker for the central air. I understand that i can remove two single pole breakers and use a tandem. Question is this? How are they wired? Do I just use the black wires from each breaker I remove and leave the white and ground where they are currently at? Thanks
Mark
 
Attached Images      

Last edited by Mark Cavinee; 03-07-20 at 11:27 AM.
  #2  
Old 03-07-20, 10:58 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Welcome to the forums.

Sometimes you can add tandem breakers for the 120v circuits in order to make room for a 2P breaker. Every panel is different. There is usually a diagram on the door that illustrates where tandems can be used.

With a picture of that and the inside of your panel we could guide you further.
How-to-insert-pictures.
 
  #3  
Old 03-07-20, 11:12 AM
M
Member
Thread Starter
Join Date: Mar 2020
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you I will get the pics.
 
  #4  
Old 03-07-20, 11:31 AM
M
Member
Thread Starter
Join Date: Mar 2020
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hope I got the pics over to you
 
  #5  
Old 03-07-20, 01:24 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,753
Received 672 Upvotes on 570 Posts
That panel does not accept tandem breakers.

However, you could just move the lower right breaker to the left side to get the two spaces you need for your two-pole 30. Just extend the existing wire with another wire of the same size to reach the new breaker location.

I should also mention that the ground wire at the bottom is not properly bonded to the panel steel.

(Thread relocated to electrical AC/DC from lighting)
 
CasualJoe voted this post useful.
  #6  
Old 03-07-20, 02:40 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,619
Received 240 Upvotes on 204 Posts
Is there another disconnect before this panel. I ask because there appears to be a four wire feed having the bare aluminum ground going the ground bar. Something seems odd with having a few circuits grounds hooked to the neutral bars. I can't see that the neutral bar is bonded. What I'm wondering is if this is a miswired subpanel.
 
CasualJoe voted this post useful.
  #7  
Old 03-08-20, 04:54 AM
A
Member
Join Date: Mar 2014
Posts: 834
Received 124 Upvotes on 104 Posts
pattenp has a point. From what I see also this seems to be a 4 wire feed indicating this is a sub panel. The braided aluminum wire going to the separate ground bar seems to be that of the feeder.

The ground bar is correct and if a 4 wire then the braided should be going to the separate ground bar as it is doing. However, all the ground wires from the neutral bars on the left and right should be moved over to the separate ground bar. Only one neutral wire per screw and up to two ground wires per screw.

A picture towards the top of the panel would help. The picture should include where the service wires are coming into the top of the panel and include in the picture the ground bar along with the hots and neutral wires. This will give us a better idea. This is a safety issue that should be dealt with.
 
CasualJoe voted this post useful.
 