securing overhead cable along multiple poles
#1
Member
Thread Starter
Join Date: Mar 2020
Posts: 5
Received 0 Votes
on
0 Posts

I have service going to a pole, then down to a meter base with a breaker. Power will then be brought back up the pole and then overhead over 2 poles (house is 110 ft from service). Iv done fiber optic wire before (different job) and at each pole we used a clamp method with the messenger wire.
https://hubbellcdn.com/prodimage1200...IMAGE_1200.jpg
Can i use this clamp on the messenger wire at each pole and use all thread through the pole to attach or will that compromise the "neutral wire. Any suggestions on what else i can or should use. yes it has to be over head.
https://hubbellcdn.com/prodimage1200...IMAGE_1200.jpg
Can i use this clamp on the messenger wire at each pole and use all thread through the pole to attach or will that compromise the "neutral wire. Any suggestions on what else i can or should use. yes it has to be over head.
#2
Technically it will be the ground wire since you will need a four wire feed after panel on the first pole.
Geochurchi voted this post useful.
#3
Member
Thread Starter
Join Date: Mar 2020
Posts: 5
Received 0 Votes
on
0 Posts
The area inspector has told me that if Fortis supplies the meter base and breaker then I only require 3 wire but if we supply the meter base and breaker we need 4 wire. Fortis has been supping the meter base more often for rural customers.
#4
Suspending service cable requires some considerations. Most aluminum service cables are not rated to be hung. You would need to get triplex cable which has a steel runner in with the bare neutral.
To utilize your method with those clamps would require you installing a guy (runner) wire first.
When I suspend triplex I use service hooks and wedge clamps.
Aluminum wedge clamps
To utilize your method with those clamps would require you installing a guy (runner) wire first.
When I suspend triplex I use service hooks and wedge clamps.
Aluminum wedge clamps
#5
The area inspector has told me that if Fortis supplies the meter base and breaker then I only require 3 wire but if we supply the meter base and breaker we need 4 wire. Fortis has been supping the meter base more often for rural customers.
#6
I also normally use the wedge clamps like PJ posted and insulated knobs with a lag bolt.
https://www.lowes.com/pd/Sigma-Elect...E&gclsrc=aw.ds
https://www.lowes.com/pd/Sigma-Elect...E&gclsrc=aw.ds
#7
Member
Thread Starter
Join Date: Mar 2020
Posts: 5
Received 0 Votes
on
0 Posts
Fortis uses a "non approved" breaker ( not sure what that means). whereas if i bought a meter base with breaker it would be " approved" and i would need 4 wire for it. Also this install is in Alberta so CEC is the rule of law.