Wiring my shed from my house

I want to run electricity to my shed from my house, it's going to be a workshop for welding and woodworking.
Can someone let me know what wire, breaker, and conduit ill need? I need to run the wire underground from my main panel to a sub-panel in the shed. the shed is about 65ft away.

The shop will have:
Welder
15 amp jobsite table saw
mitresaw
2 led lights
4 receptacles

Thanks a lot.
 
Sponsored Links
  #2  
Old 04-02-20, 08:58 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,325
Received 190 Votes on 168 Posts
60 amp sub panel should be fine unless you have some sort of huge welder.
 
  #3  
Old 04-03-20, 05:05 AM
Marq1's Avatar
Member
Join Date: Sep 2016
Location: USA MI
Posts: 5,663
Received 241 Votes on 228 Posts
Need to verify the welder requirements, it's the big amp draw!
 
  #4  
Old 04-03-20, 05:52 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,318
Received 45 Votes on 38 Posts
Knowing what size welder you want to run does help deciding the feed size. That being said I believe a 60A feed will most likely suit your needs with no problem. I would use 3 conductors of #4 Al XHHW-2 and 1 conductor of #8 Al XHHW-2 for the feed wires fed from a 60A breaker in the main panel. As a minimum use 1 inch PVC conduit. Individual conductors need to be in conduit from panel to panel. Get a small 100A Main breaker panel for the subpanel. You need to place 2 ground rods at the shed 6ft apart on a single #6 Cu conductor hooked to the ground bar in the subpanel. Most likely you'll need to buy a ground bar kit for the subpanel because the neutrals need to be isolated from grounds which means removing the bonding strap from the neutral bar to the subpanel case.

Edit: Conduit need to be buried with 18 inches of cover. Knowing your location would help. Code requirements differ based on location.
 

Last edited by pattenp; 04-03-20 at 06:25 AM.
  #5  
Old 04-03-20, 09:49 AM
N
Member
Thread Starter
Join Date: Apr 2020
Posts: 4
Received 0 Votes on 0 Posts
I was under the impression a 40 amp breaker in the main panel and a #8 nmd90 in the conduit to the shed is sufficient.
 
  #6  
Old 04-03-20, 09:55 AM
N
Member
Thread Starter
Join Date: Apr 2020
Posts: 4
Received 0 Votes on 0 Posts
  #7  
Old 04-03-20, 10:17 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,308
Received 133 Votes on 117 Posts
Conductors or cables installed in wet locations (conduit outside or buried is a wet location) is required to be rated for wet locations. I do not think NMD90 is rated for wet locations.

40 amp will likely be fine as that is all I have to my shop. However, that would be close to the limit. I agree with Joed and install #6 copper wire and a 60 amp fuse/breaker.
 
  #8  
Old 04-03-20, 11:34 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,318
Received 45 Votes on 38 Posts
Being 65ft you should consider aluminum. There is nothing wrong with the use of aluminum conductors when doing a feeder. The cost is less than half of copper. Do not let issues of aluminum of years ago worry you. Today's aluminum alloy for wire is safe.
 
  #9  
Old 04-03-20, 12:21 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,308
Received 133 Votes on 117 Posts
Today's aluminum alloy for wire is safe.
When properly installed.
 
  #10  
Old 04-03-20, 02:12 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,325
Received 190 Votes on 168 Posts
NMD90 is for dry. You can't use that underground in conduit. You need NMW for wet locations.
 
  #11  
Old 04-03-20, 02:38 PM
N
Member
Thread Starter
Join Date: Apr 2020
Posts: 4
Received 0 Votes on 0 Posts
Shoot! I wish I knew that before I bought the cable. I got nmd90 my friend in school for electrical said that would be good because my only other option at the store was #8 nmw60. he said I shouldn't get anything rated lower than 75 degrees. Shouldn't have listened to him I guess.
 
  #12  
Old 04-03-20, 03:10 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,325
Received 190 Votes on 168 Posts
Also ground rods are not required for detached buildings in Canada.

Add your location to your profile. It helps quoting the proper rules.
 
  #13  
Old 04-03-20, 03:41 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,318
Received 45 Votes on 38 Posts
When properly installed.
The same can be said for copper.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: