wire size 250'

So I'm wiring up a 200 amp panel 250' away from pole 3 wire 120v. Just wanted to make sure I am running the correct wire which I calculated to be aluminum 600 mcm for a max 3% voltage drop. It seems large to me which is why I am here.

Any help appreciated!
 
  #2  
Old 04-21-20, 06:55 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,298
Received 110 Votes on 102 Posts
When calculating resistance of the wiring run, don't forget to use round trip distance. Unfortunately some voltage drop calculators already include that compensation and some don't so it can be confusing.

For standard 120/240 volt services and feeders use 240 volts and not 120 in your calculations.

For simplicity, voltage drop calculations are watered down. Calculation result is based on full load at 240 volts.

 
  #3  
Old 04-21-20, 10:01 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
Does the 200A panel have the first disconnect after the meter? Or is there a disconnect back at the pole? I'm asking because oneway is 3 wire feeder, the other requires a 4 wire feeder.
 
  #4  
Old 04-21-20, 11:34 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,936
Received 1,351 Votes on 1,249 Posts
120/240v - single phase - one way distance 250' - 3% max drop.

According to the calculator I use..... you will need to run 250mcm aluminum or 3/0 copper
 
  #5  
Old 04-21-20, 12:21 PM
T
Member
Join Date: Oct 2005
Location: USA
Posts: 1,693
Received 47 Votes on 46 Posts
I get 2.68% drop at 240V and 200A with 250kcmil copper.
 
  #6  
Old 04-21-20, 12:32 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
Here is the equation for VD: 2 x I x R / 1000 * FT = VD / 240 = voltage drop % (at 240v)

2 x 200 x .0847 = 33.88

33.88/1000 = .03388
.03388 x 250 = 8.47
8.47 / 240 = 3.52% total drop for 200A on 250' of 250kcmil AL
R is .0847 at 75deg.C for 250 kcmil Al per NEC Table 8

300 kcmil Al with R at .0707 will be 3% VD.
 
  #7  
Old 04-21-20, 12:32 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,572
Received 161 Votes on 143 Posts
Does the service wiring need to be sized to the full 200A? Have you done a demand load calc? Unless you're running electric heat or on-demand water heaters, most houses don't use anywhere near the 200A max. You may be able to down-size the cabling if your usage is lower than 200A.

(I believe you can adjust your wire size based on projected load for a service)
 
  #8  
Old 04-22-20, 10:35 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,765
Received 97 Votes on 87 Posts
Where is the meter, on the pole or at the structure where the 200 amp panel is located??
 
 