Does breaker size matter for this?
#1
Does breaker size matter for this?
I have a GFCI with a waterproof cover that I ran outside to the end of my yard on a fence post so I can plug in a bug zapper or have a powered outlet if I need one when BBQing or hosting a get together. I used Type UF-B 12/2 and ran it 2 feet underground and then into my garage to a light switch then from the switch to my main house panel. The switch is so I can have the bug zapper plugged in and just go in my garage and flip the switch to power it, instead of walking all the way outside each night I choose to have it on. I have everything wired up and done except I have not added the wires in the panel to a breaker yet. I was going to buy a 20amp because I didnt really think about it but someone told me I should run something like that to a 15amp instead. I didn't really understand the reason why, but he made it sound like I could somehow damage the line by using a 20amp instead of a 15amp because it would send it more power. But my understanding of power is a 20 amp LIMITS it to 20 amps but it doesn't matter if I have a 20amp or 15amp. As an example, If i have a device that draws 10amps it won't matter if I have a 20 or a 15 connected to it because it should only draw the 10, so I just thought a 20 would be on the safer side for a industrial type bug zapper. (Correct me if I am wrong please)
I don't claim to be an expert on electrical but I think my friend is an idiot so I just decided to confirm if it matters what breaker amp I buy to attach to my panel.
I don't claim to be an expert on electrical but I think my friend is an idiot so I just decided to confirm if it matters what breaker amp I buy to attach to my panel.
#2
When it comes to safer.... a 15A is safer than a 20A breaker as it will trip quicker on an overload.
However.... with #12 wiring..... you can use a 20A breaker safely.
However.... with #12 wiring..... you can use a 20A breaker safely.
#3
Thank you for the reply PJmax, I think I read that my bug zapper draws 4amps so if from what you are saying, if that is the biggest thing I ever plan to have plugged into it I should go lower, even maybe to a 10 amp for safety? I was thinking about running a heated dog bowl during the winter for my ducks but I doubt that would draw more than 10 amps.
#5
Most appliances and devices are rated to be plugged into a 15A or 20A circuit.
So there would not be a need to size the circuit for a particular device or load.
So there would not be a need to size the circuit for a particular device or load.
#7
telecom guy
Can you estimate the length of the entire run. Receptacle to breaker?
Can you estimate the length of the entire run. Receptacle to breaker?
#8
Put a 20A breaker on that new line. This way if in the future you want to plug something in a little larger..... you don't have to worry about a breaker tripping.
#11
Trying to pull 20A on a 135foot line can result in burned out motors
#12
Like PJmax said, I already ran the line. The biggest thing I plan to plug into it (as of right now) is a 100 watt bug zapper so I would be skeptical if a 20 amp tripped over that. But then again, I am not a professional.