Old panel to new panel to wire trough via 2" PVC
Code compliance question; can I do this in my basement?
SEE ATTACHED PICTORIAL
- Add additional basement breaker panel alongside my exiting one. (No more breaker room on the existing panel.)
- Jump old panel to new panel with what ga wire? Old panel: 100 amp. New panel already has 100 amp mains breaker. Breaker size on old panel?
- Build 2" PVC out of new panel to a rafter mounted 6" x 6" x 36" wiring trough. Why? There's no room on right side of new panel for easy new Romex circuits installation.
- Run bare copper ground (4 or 6 ga?) from new panel to ground bus terminal strip in wire trough via the 2" PVC. Terminate all grounds in trough to ground bus.
- Run all new circuits from wire trough to new panel through the 2" PVC using 12 ga. wire (black/white) pairs.
SEE ATTACHED PICTORIAL
#2
Build 2" PVC out of new panel to a rafter mounted 6" x 6" x 36" wiring trough. Why? There's no room on right side of new panel for easy new Romex circuits installation.
I generally always try to avoid creating a Rube Goldberg.
#3
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 68
Received 0 Votes
on
0 Posts
The new panel is already mounted next to the old panel with a temp jum from the old to the new.
The wire trough was installed some time ago.
The current installation is a Rube Goldberg. (Rube was well intentioned, but his work could kill you. You've been there.)
I need to finish up this project -the right way.
I don't want an inspector to say, rip this out before I sell my house.
I just want to meet/exceed Code.
I also do VERY neat work.
Many thanks!
The wire trough was installed some time ago.
The current installation is a Rube Goldberg. (Rube was well intentioned, but his work could kill you. You've been there.)
I need to finish up this project -the right way.
I don't want an inspector to say, rip this out before I sell my house.
I just want to meet/exceed Code.
I also do VERY neat work.
Many thanks!
#4
If the 2" conduit is more than 24" then you have to take derating into account and then you are pretty much limited to 9 current-carrying conductors. If it is less than 24" it is considered a nipple and you can fill the pipe to 60%.
Breaker size in the main panel? It depends on what size wire you want to use or how many amps you want available to the sub-panel. I would recommend three #6 wires, one #10 ground, and a 60 amp breaker.
Ground wire to the gutter will depend on the largest conductor in the pipe. If it is #12 then you only need to use a #12 for the ground.
Breaker size in the main panel? It depends on what size wire you want to use or how many amps you want available to the sub-panel. I would recommend three #6 wires, one #10 ground, and a 60 amp breaker.
Ground wire to the gutter will depend on the largest conductor in the pipe. If it is #12 then you only need to use a #12 for the ground.
#7
the derate issue.might kill the wire trough idea. I was hoping to accommodate more circuits in the 2".
#12
It's typical to solve your problem with separate NM-B cables from the panel to a junction box in the ceiling (accessible), then out to the circuits. It happens when the cables aren't long enough.
It could be a couple double-gang plastic new work boxes, a couple 4x4 metal boxes, or a larger 6x6 or 8x8 box if you'd rather. All are rather usual to see in a setup like this.
Due to the derating requirements, making it look all neat with conduit and trough isn't usually done in residential settings.
It could be a couple double-gang plastic new work boxes, a couple 4x4 metal boxes, or a larger 6x6 or 8x8 box if you'd rather. All are rather usual to see in a setup like this.
Due to the derating requirements, making it look all neat with conduit and trough isn't usually done in residential settings.