Circuit stop working after thunderstorm

Hi,

After some bad weather last night where we lost power, once the power came back on, one of the circuits no longer works. It's a 15 amp AFCI circuit, with a bunch of receptacles and some switches. I tested the breaker, showed 120V. I tried another circuit breaker, still no power to the circuit.

I pulled one of the outlets to test, showing no continuity and no voltage. Everything worked fine prior to losing power, for the last 8 years, so I'm guessing the storm damaged something (fried a wire or something?). Just not sure about next steps, any advice much appreciated.

Thanks,

Dan
 
  #2  
Old 05-16-20, 06:02 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,734
Received 300 Votes on 257 Posts
What is on the circuit? Are there any GFCI? Electrical storms can sometimes trip a GFCI.
 
aerodan1 voted this post useful.
  #3  
Old 05-16-20, 06:08 PM
A
Member
Thread Starter
Join Date: Aug 2012
Posts: 127
Received 0 Votes on 0 Posts
Good question, but just double checked, no GFCIs
 
  #4  
Old 05-16-20, 06:10 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,936
Received 1,351 Votes on 1,249 Posts
Check for 120vAC from the small slot to ground at one of the receptacles.
You may have an open neutral.
 
aerodan1 voted this post useful.
  #5  
Old 05-16-20, 06:28 PM
A
Member
Thread Starter
Join Date: Aug 2012
Posts: 127
Received 0 Votes on 0 Posts
PJ, no voltage from ground to hot lead
 
  #6  
Old 05-16-20, 06:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,936
Received 1,351 Votes on 1,249 Posts
Ok....so it's not specifically a loss of neutral.
That leaves you to open every dead box to check for a problem.
This is a perfect application for a non-contact tester. You can test without even opening the box.

What I do is picture how the circuit is laid out.
Then I go to the closest point/box to the panel and start checking there.
 
aerodan1 voted this post useful.
  #7  
Old 05-16-20, 06:47 PM
A
Member
Thread Starter
Join Date: Aug 2012
Posts: 127
Received 0 Votes on 0 Posts
Thanks again, PJ. Unfortunately I think they are all tamper resistant outlets, so the noncontact tester doesn't insert. Maybe i can just take the covers off and test the terminals.
 

Last edited by aerodan1; 05-16-20 at 07:05 PM.
  #8  
Old 05-16-20, 07:15 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,936
Received 1,351 Votes on 1,249 Posts
My tester picks up without it being in the slots.
Also depends on metal and non metallic plates.
You can remove the plate and stick the nose of the tester into the box.
 
  #9  
Old 05-16-20, 10:59 PM
A
Member
Thread Starter
Join Date: Aug 2012
Posts: 127
Received 0 Votes on 0 Posts
I tested all of the outlets and switches, no voltage on any of them. Wondering what the next step is.

I guess maybe I should do a closer inspection of each outlet and switch to make sure no broken or loose wires. Maybe try replacing the first outlet or switch on the circuit.
 
  #10  
Old 05-16-20, 11:53 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,936
Received 1,351 Votes on 1,249 Posts
If you didn't get tick inside the box.... the power is not there.
Did you check the breaker with an actual meter or two probe test light ?
A non contact tester won't work for that test.
 
aerodan1 voted this post useful.
  #11  
Old 05-17-20, 12:11 PM
A
Member
Thread Starter
Join Date: Aug 2012
Posts: 127
Received 0 Votes on 0 Posts
Hi PJ, Yes, I checked the voltage for the breaker using a multimeter. I also tried replacing a few of the switches and outlets on that circuit last night to see if that would help, but it didn't.
 
  #12  
Old 05-17-20, 03:55 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,734
Received 300 Votes on 257 Posts
What does this circuit supply? To me it still sounds like a GFCI that you haven't found. Outside? Behind a pile of boxes in the garage or basement?
 
  #13  
Old 05-17-20, 09:55 PM
A
Member
Thread Starter
Join Date: Aug 2012
Posts: 127
Received 0 Votes on 0 Posts
Joed, This circuit is for two bedrooms, mostly receptacles and a couple of switches, as well as the lights in two bathrooms. No gfci Outlets

Update: The problem has been solved. I took another look at the wiring diagram I had drawn, and remembered that I had added an outlet in the attic on the circuit. That outlet was a GFCI and of course had tripped.

Thank you all so much!
 

Last edited by aerodan1; 05-17-20 at 10:23 PM.
  #14  
Old 05-17-20, 11:18 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,734
Received 300 Votes on 257 Posts
The attic receptacle should be rewired so that nothing is connected to the LOAD terminals. That way only the GFCI itself goes dead and not the entire circuit.
 
aerodan1 voted this post useful.
  #15  
Old 05-18-20, 03:07 PM
A
Member
Thread Starter
Join Date: Aug 2012
Posts: 127
Received 0 Votes on 0 Posts
Joed, great point! If I run a pigtail instead of connecting directly to the load terminal, will save the hassle of having to go up into the attic if it trips again. Thanks
 
  #16  
Old 05-18-20, 05:31 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,734
Received 300 Votes on 257 Posts
GFCI usually have a clamp style screw. You can put two wires under the clamp, one on each side. You should be able remove the wire from the LOAD and move it to the LINE.
 
aerodan1 voted this post useful.
 