Wire size


  #1  
Old 05-26-20, 03:51 AM
P
Member
Thread Starter
Join Date: May 2020
Posts: 1
Received 0 Votes on 0 Posts
Wire size

Going to run electric from my house to my garage, what size wire would i need for a 125amp panel? It's about 100ft from house to garage?
 
  #2  
Old 05-26-20, 04:19 AM
Norm201's Avatar
Member
Join Date: Sep 2013
Location: United States
Posts: 11,421
Received 595 Votes on 532 Posts
12 gauge with a 20 amp breaker. That will handle most power tools. The 100 feet is not so much. Think about the length of wire going throughout the house. 100 feet is not excessive.
 
  #3  
Old 05-26-20, 04:38 AM
C
Member
Join Date: Mar 2007
Posts: 2,319
Received 228 Votes on 186 Posts
I'm not an electrician but I would use 2 ga wire as a minimum. Are you sure you need such a large panel in the garage?
 
  #4  
Old 05-26-20, 06:24 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,850
Received 210 Votes on 178 Posts
For 125A #2/0 aluminum will do nicely. One of the best options is 2/0-2/0-2/0-1 MHF. MHF is direct bury but would be best in conduit all the way panel to panel. It does have to be in conduit where above ground including inside. If you don't want direct bury cable use XHHW-2 AL wires in the same sizes.
 
  #5  
Old 05-26-20, 08:15 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 11,151
Received 164 Votes on 147 Posts
what size wire would i need for a 125amp panel?
That would depend on how many amps you will be feeding the panel with. Just because the panel is rated for 125 maximum amps doesn't mean you have to feed it with 125 amps. What will you be using the electric in the garage for? For most people 60 amps would be more than adequate. It hasn't been so many years ago that there were still plenty of older homes that only had 60 amps for the entire house.
 
  #6  
Old 05-26-20, 12:17 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,850
Received 210 Votes on 178 Posts
Casualjoe makes a very good point. If you decide you do want a 125A feed to the garage make sure your main house panel can take a 125A breaker, some panels you may find are limited to 100A breakers for branch circuits. Another popular feeder is 2-2-2-4 MHF which is good for up to 90A but is commonly fed from a 60A breaker because the 60A breaker is usually a lot cheaper than the 90A breaker. You can always up the breaker size to 90A if more power is needed later. Some inspectors will allow a 100A breaker on the #2 Al, but as a sub feeder technically only a 90A max breaker is allowed by the NEC.
 
 