GFCI 20 AMP breaker tripping


  #1  
Old 05-28-20, 05:45 AM
P
Member
Thread Starter
Join Date: May 2020
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
GFCI 20 AMP breaker tripping

From the main house there is a 100AMP service to a shop about 160 ft run there is a 10-2 wire from the electrical panel in the shop going to an outlet that has a 20 AMP outlet with a 20 AMP GFCI breaker this is the only outlet that is on that breaker however anytime I use a tool such as my miter Saw or my welder it seems that the breaker keeps tripping I don’t remember what the electrician said about the 160 foot run but he did say it was an upgrade to what normally would be in a 100 amp service box due to the length of the cable to run from the house to the shop Any advice on what could be the cause or how to resolve this issue
 
  #2  
Old 05-28-20, 06:50 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 3,034
Received 275 Upvotes on 245 Posts
A GFCI does not trip on overcurrent, so either the GFCI is defective or both of your appliances have a leakage path for the current. Do you have another GFCI where you can test the appliances for proper operation?
 
  #3  
Old 05-28-20, 07:18 AM
P
Member
Thread Starter
Join Date: May 2020
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Gfci

I do not have another outlet that would work however I do have another 20 AMP GFCI breaker I can switch it out to see if that solves the problem
 
  #4  
Old 05-28-20, 08:47 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,842
Received 179 Upvotes on 162 Posts
A GFCI does not trip on overcurrent,
This one does, it's a 20 amp GFCI breaker, not a GFCI receptacle.
 
beelzebob voted this post useful.
  #5  
Old 05-29-20, 06:24 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 3,034
Received 275 Upvotes on 245 Posts
Thanks for the update Casual Joe. I misunderstood the configuration.
 
 