Wiring a 100A sub panel
Old 07-07-20, 08:41 PM
A
Good Evening,
I am wiring a 100A square D sub panel off a GE PowerMark Plus 150A main panel. Im using 2 gauge wire, and I was looking for a place in the main panel to attach a neutral lug kit to the bus bar for the neutral. I noticed that next to the main neutral feed, there was an available lug. Is it possible to utilize that instead of attaching to bus bar? See attached pictures.
Thanks.
Old 07-07-20, 08:45 PM
Received 906 Votes on 846 Posts
Welcome to the forums.
Yes.... you can use that lug for the neutral connection for you sub panel.
Don't forget since it's a sub panel you'll need to run 4 wires.... 2 hots, a neutral and a ground.
You'll need a location to attach the ground wire.
Old 07-07-20, 09:06 PM
L
Received 50 Votes on 46 Posts
I see you have GE panel, but has non-GE breakers. All breaks should be GE THQL or THQP (thin breakers).
CasualJoe voted this post useful.
Old 07-08-20, 08:09 AM
P
Received 58 Votes on 47 Posts
Also just a fyi, if the feeder is #2 aluminum the max feeding breaker by the NEC is 90A.
Old 07-08-20, 05:05 PM
CasualJoe's Avatar
Received 71 Votes on 62 Posts
I'm using 2 gauge wire,
I hope that's copper. I'd use either #3 copper or #1 aluminum.
Old 07-13-20, 04:09 AM
A
Yes Im running copper all around, no aluminum, also the distance is approximately 5 ft.