Breaker keeps tripping


  #1  
Old 07-20-20, 01:37 AM
M
Member
Thread Starter
Join Date: Jul 2020
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Breaker keeps tripping

Same breaker has tripped every day in the early a.m. at same time for 4 days. Once reset, it stays on until same time in the a.m. and then trips again. Replaced the breaker. What am I missing? I plugged in and turned everything on in house systematically to see if breaker would trip in the afternoon and nothing happened. Replaced old surge protectors and 3 receptacles. Breaker still is tripping.
 
  #2  
Old 07-20-20, 03:35 AM
A
Member
Join Date: Mar 2014
Posts: 835
Received 124 Upvotes on 104 Posts
Is it a regular circuit breaker opposed to one that is a GFCI or AFCI - does it have a reset button on it.

Also, not knowing your skill level how comfortable are you working inside of a panel. If you have never done so then fine - don't. If you have maybe switching the lead hot wire going to this circuit breaker to another circuit breaker of the same kind (matching amp rating). Seeing if this same issues happens again. Trying to eliminate the fact that maybe the breaker is going bad (but unlikely), breakers don't normally go bad easily.

Also is it possible that this circuit services an appliance of pump or something like that that may be in a timer?
 
  #3  
Old 07-20-20, 04:41 AM
the_tow_guy's Avatar
Group Moderator
Join Date: Feb 2001
Location: SW Fla USA
Posts: 11,983
Received 176 Upvotes on 138 Posts
As AFJES noted, important to know exactly which circuit it is and what devices are on that breaker. Start there and narrow it down.
 
  #4  
Old 07-20-20, 04:49 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
It seems to me that something is turning on at 4 am and tripping the breaker.
 
  #5  
Old 07-20-20, 09:41 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,833
Received 367 Upvotes on 327 Posts
Usually, it's something turning on at 4am as joed mentioned. Coffee maker, pool pump, outdoor lights, etc.

But could be something more complicated too. Worked somewhere a while back that had an electronic lighting system that went haywire every Wednesday evening. Looong story short, issue was possibly traced back to the power company doing some kind of generator switching likely causing some weird harmonics that messed with a poorly grounded/bonded system.

Granted, your situation is probably more benign than that, but starting point is to figure out what's connected to that breaker and disconnecting all of it or some of it and see what happens the next day.
 
 