wiring pole barn


  #1  
Old 07-25-20, 01:29 PM
H
Member
Thread Starter
Join Date: May 2009
Location: central
Posts: 57
Upvotes: 0
Received 0 Upvotes on 0 Posts
Smile wiring pole barn

am going to add (2) 20amp breakers in our pole barn because adding some tools. adding a air compressor and table saw. have a 20amp in box already and have be using a table saw and miter saw. I just wanted to spread out the load and move some outlets around. have been having problems finding 20amp outlets and gfi. I took the covers off the original outlets and found that they and the GFI are 15amps..off a 20amp breaker. what I would like to know now is how do I run these new outlets....all 15amps off a 20amp breaker or what....
 
  #2  
Old 07-25-20, 01:54 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 6,095
Received 422 Upvotes on 375 Posts
Code allows 15A receptacles (GFI or standard) on a 20A circuit. All GFI devices are rated for 20A feed-through.

The only time a 20A receptacle is required is if you either have a device that has a 20A plug (NEMA 5-20), or if it's a dedicated circuit with only one receptacle/plug on a 20A circuit. (Note that a duplex receptacle counts as 2, so doesn't fall into this requirement).
 
CasualJoe voted this post useful.
  #3  
Old 07-26-20, 07:51 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
All GFI devices are rated for 20A feed-through.
As are 15 amp rated duplex receptacles.
 
Zorfdt voted this post useful.
 