Generator grounding
#1
Generator grounding
So as not to hi-jack WRDIY's post (https://www.doityourself.com/forum/o...ml#post2859396), I stated a new thread.
CWBuff replied to WRDIY thread to my question...
Quote:
If I understand the grounding requirements correctly a portable generator need not be separately grounded except when it is providing power to a house through a transfer switch.
My reply "It's my understanding that if it's bonded then that requirement is not needed, because grounding takes place at the house transfer switch. Am I wrong?"
CW again replied with..."I found this article that quotes OSHA requirements - https://www.jadelearning.com/blog/gr...le-generators/"
Which I read.
I'm still confused.
My generator/inverter (Ryobi model i2300 with floating neutral) is connected directly to my cabin's circuit box. I asked the question back in Nov this past year (https://www.doityourself.com/forum/e...grounding.html) and was advised that a grounding rod was not necessary, grounding would take place via the cabin electrical box.
I also have a Coleman Powermate (PM0435001 with floating neutral) hook to my home via transfer switch but not grounded with a rod at the generator. Should I?
Thought I had this sorted out.
CWBuff replied to WRDIY thread to my question...
Quote:
If I understand the grounding requirements correctly a portable generator need not be separately grounded except when it is providing power to a house through a transfer switch.
My reply "It's my understanding that if it's bonded then that requirement is not needed, because grounding takes place at the house transfer switch. Am I wrong?"
CW again replied with..."I found this article that quotes OSHA requirements - https://www.jadelearning.com/blog/gr...le-generators/"
Which I read.
I'm still confused.
My generator/inverter (Ryobi model i2300 with floating neutral) is connected directly to my cabin's circuit box. I asked the question back in Nov this past year (https://www.doityourself.com/forum/e...grounding.html) and was advised that a grounding rod was not necessary, grounding would take place via the cabin electrical box.
I also have a Coleman Powermate (PM0435001 with floating neutral) hook to my home via transfer switch but not grounded with a rod at the generator. Should I?
Thought I had this sorted out.

#2
No ground rod is needed at the gen when the gen is connected to a house electrical system. The earth ground is provided by the house electrode system. There needs to be a equipment ground connection from the gen to the house. You may be confused about the equipment ground vs. the electrode ground to earth. Electrode is for diverting lightning strikes whereas the equipment ground is for cleaning fault current. Floating neutral on the gen is correct.
#5
OK, understood. And how does bonded or unbonded affect that scenario?
Also if the generator is connected to the house, even though it's not providing power to the house, but I'm using one of the taps to say run a skill saw outside, do I need to ground the unit with a rod?
Also if the generator is connected to the house, even though it's not providing power to the house, but I'm using one of the taps to say run a skill saw outside, do I need to ground the unit with a rod?
#6
OK, understood. And how does bonded or unbonded affect that scenario?
Also if the generator is connected to the house, even though it's not providing power to the house, but I'm using one of the taps to say run a skill saw outside, do I need to ground the unit with a rod?
Pros please correct me if I'm mistaken!
Edit: I'm assuming your connection to the house doesn't switch off the ground when the generator is connected, but house is running on PoCo power. In an interlock setup, only the hots are switched off, the ground and neutral remain in place.
#8
This is what my generator manual says - " If this generator is used only with cord and plug connected equipment, National Electric Code does not require that the unit be grounded." That seems clear. If you are running off plug ins (i.e. tools or extension cords) no separate ground is required.
It is less clear about other circumstances. In those instances the manual simply says "Other methods of using the generator may require grounding . . . . . " "Consult an electrician." My assumption of a common other circumstance would be a generator wired to a transfer switch.
I think both those statements agree with the OSHA requirement.
It is less clear about other circumstances. In those instances the manual simply says "Other methods of using the generator may require grounding . . . . . " "Consult an electrician." My assumption of a common other circumstance would be a generator wired to a transfer switch.
I think both those statements agree with the OSHA requirement.
#9
Mike Holt has an excellent (but long) video that explains about floating neutral vs bonded neutral generators in minute detail. It's worth a watch for sure.
https://www.youtube.com/watch?v=yS7usLY9zL4&t=116s
https://www.youtube.com/watch?v=yS7usLY9zL4&t=116s