Is this acceptable to code? (Pic)
#1
Member
Thread Starter
Is this acceptable to code? (Pic)
Is this an acceptable way to extend off an outlet in the middle of a circuit to install a new outlet? Installing two wires under the same screw clamp. Or would it have to be pig tails? I’ve come across a few instances where someone added a 3rd wire by using the push-in connector as well as both screws so my thinking is this would be better than that.


#3
#7
Member
Thread Starter
#9
Technically, it's not a code issue, but related to the instructions/approvals on the receptacle.
UL has this to say:
https://legacy-uploads.ul.com/wp-con...NovDec2008.pdf
So assuming that receptacle is UL listed, you're using it as intended.
UL has this to say:
The Guide Information for (RTRT) states single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have been investigated to feed branch-circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
• Back wire (screw actuated clamp type) terminations with multiple wire access holes used concurrently to terminate more than one conductor
• Back wire (screw actuated clamp type) terminations with multiple wire access holes used concurrently to terminate more than one conductor
So assuming that receptacle is UL listed, you're using it as intended.