Is this acceptable to code? (Pic)

Is this an acceptable way to extend off an outlet in the middle of a circuit to install a new outlet? Installing two wires under the same screw clamp. Or would it have to be pig tails? I’ve come across a few instances where someone added a 3rd wire by using the push-in connector as well as both screws so my thinking is this would be better than that.



 
  #2  
Old 08-24-20, 03:41 PM
Norm201's Avatar
Member
Join Date: Sep 2013
Location: United States
Posts: 9,492
Received 292 Votes on 262 Posts
I'm not an authority on this. But I believe with this type of clamp vs hook and screw OK. But not if two wires are actually being hooked and screwed under the same terminal.
 
  #3  
Old 08-24-20, 05:41 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,924
Received 1,347 Votes on 1,245 Posts
That method is much better than using the push-in but the ideal method is to tail it.
 
cartman voted this post useful.
  #4  
Old 08-24-20, 05:58 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,733
Received 300 Votes on 257 Posts
Those are clamp style. It is perfectly fine to have two wires per screw as pictured.
 
Norm201 voted this post useful.
  #5  
Old 08-25-20, 05:17 AM
Norm201's Avatar
Member
Join Date: Sep 2013
Location: United States
Posts: 9,492
Received 292 Votes on 262 Posts
But not if two wires are actually being hooked and screwed under the same terminal.
Will the experts confirm if this is not proper. Thanks.
 
  #6  
Old 08-25-20, 05:57 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,733
Received 300 Votes on 257 Posts
The clamp style as pictured is fine.
Wrapping two wires around and under the screw is not fine.
 
Norm201 voted this post useful.
  #7  
Old 08-25-20, 06:44 AM
S
Member
Thread Starter
Join Date: Aug 2020
Location: United States
Posts: 13
Received 0 Votes on 0 Posts
Norm201 I am not an expert but I’ve seen in a lot of places never to loop two wires under the same screw because it wasn’t designed for more than one wire and could result in a poor connection, fire hazard.
 
  #8  
Old 08-25-20, 06:56 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: United States
Posts: 4,964
Received 88 Votes on 83 Posts
Hi, that terminal is rated for 2 conductors, stay away from the back stab option.
Geo
 
  #9  
Old 08-25-20, 11:10 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,569
Received 161 Votes on 143 Posts
Technically, it's not a code issue, but related to the instructions/approvals on the receptacle.

UL has this to say:
The Guide Information for (RTRT) states single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have been investigated to feed branch-circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
Back wire (screw actuated clamp type) terminations with multiple wire access holes used concurrently to terminate more than one conductor
https://legacy-uploads.ul.com/wp-con...NovDec2008.pdf

So assuming that receptacle is UL listed, you're using it as intended.
 
 