Feeder size sanity check

Reply

  #1  
Old 09-03-20, 10:33 AM
T
Member
Thread Starter
Join Date: Oct 2005
Location: USA
Posts: 1,693
Received 47 Votes on 46 Posts
Feeder size sanity check

My plan is to run THHN AWG12 breakered at 25Amps as a feeder to a subpanel. All terminations are rated at 75 deg. Various 240 and 120 circuits out of the panel breakered at 20A or less each. No continuous loads over 13A.

TIA
 
  #2  
Old 09-03-20, 12:55 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,513
Received 124 Votes on 98 Posts
#12Cu is limited to 20A per NEC 240.4(D)
 
  #3  
Old 09-03-20, 01:36 PM
T
Member
Thread Starter
Join Date: Oct 2005
Location: USA
Posts: 1,693
Received 47 Votes on 46 Posts
OK, got it. ............
 
 