1 box 2 breakers, help!

i will try to keep this short and to the point.

i just discovered 1 connector box with 2 cables from 2 separate breakers. both the hot (black) are connected together and both the neutral (white) are connected together.

is this acceptable? is this safe? why would this be done? is this someones mistake? or is this a common practice?
seems unnecessary to me.? but i could be wrong
 
  #2  
Old 10-28-20, 05:23 AM
L
Member
Join Date: Nov 2015
Posts: 1,555
Received 93 Votes on 81 Posts
That is wrong. Someone probably made a mistake. 2 different sources can be in the same box, but has to be kept separate. Otherwise, the breaker will not trip properly on overload. Only the ground wire should be connected together.
 
joed voted this post useful.
  #3  
Old 10-28-20, 01:25 PM
C
Member
Thread Starter
Join Date: Oct 2020
Posts: 2
Received 0 Votes on 0 Posts
thank you!
that is what i thought, i will remedy this asap.
 
 