awg 10 into a 100 amp panel
Old 11-05-20, 03:36 PM
T
Received 68 Votes on 64 Posts
Per the title, I'm feeding 10 gauge into a 100A QO panel. The panel rates a min wire size of 8 to the lugs. Are there crimp on ferrules to bring up the conductor size? Or, I am looking at having to use a Polaris connector, or??
Old 11-05-20, 03:54 PM
Received 2,966 Votes on 2,676 Posts
Are you guilty of underfeeding an electric panel.
I don't think a crimp on ferrule is the best way to go.
Bugging on larger wires is one way to handle it.
Old 11-05-20, 04:30 PM
L
Received 170 Votes on 146 Posts
Back feeding 30A breaker probably is easier. That is unless you don't have any space left..
Old 11-05-20, 04:42 PM
T
Its a 8x12 shed, with pretty low total Amps required. Backfeeding could work. There is a 20A 240v compressor load.
On the other end of the equation, I have a 3/8" dia (29 x 16 awg) lightning rod down conductor to land somewhere. Its going to head down a wall at the subpanel, on its way to the UFER and two ground rods currently under 2 feet of cement with a solid 6 AWG headed up to the subpanel. So that guy clearly won't land inside the panel, but I need to find a clamp to accommodate that one. It seems the lightning protection world is not very related to the electrician world.
Old 11-05-20, 05:14 PM
CasualJoe's Avatar
Received 164 Votes on 147 Posts
I would also lean toward backfeeding a 30 amp breaker, but technically you should also have a main breaker hold down kit installed.
Old 11-08-20, 03:14 AM
pcboss's Avatar
Received 148 Votes on 131 Posts
No need for a lug. Simply splice on a piece of #8 or 6 with a large blue wirenut.