Reload this Page >
Understanding isolated (unbonded) neutrals and grounds in panels/subpanels
Old 11-21-20, 09:48 AM
H
I have a question regarding the isolation of grounds and neutrals in a sub panel. First, please bear with me as I describe what I see in the panels associated with my home.
I live in a mobile home. My meter feeds directly into a 200-amp cutoff panel. Within that panel are two, 100-amp breakers. One 100-amp breaker feeds the 100-amp house panel (connects to a 100-amp breaker in the house panel). The other 100-amp breaker feeds another panel (subpanel) also on the pole to a 100-amp breaker. The subpanel contains two, 20-amp DPDT breakers, one to 240V. greenhouse heaters, the other to a 240-volt circuit in a workshop (two separate buildings).
The main cutoff panel has one neutral bar, no ground bar, a buried ground rod, and an RMC to the house. The meter neutral wire and the ground wire are connected to the one neutral bar. There is also a 20-amp receptacle breaker in the cutoff panel whose neutral also connects to the neutral bar.
At the house panel, (a 1988 ITE panel) the cables from the cutoff panel connect to a 100-amp breaker, the neutral bar, and an isolated (not bonded) ground bar. The neutral and ground wires are wired to their respective bars. It seems to me that the house panel is wired as a subpanel. The first question I have is, can we make any assumptions about the ground wire if everything was done according to code at the time? Would the ground wire attached to the neutral bar in the cutoff panel be attached to a dedicated ground rod (or the RMC), and the ground wire in the house panel be attached to its own dedicated ground rod – or – would the house be sharing the cutoff panel ground.?
The subpanel to the outbuildings is connected to the cutoff panel by an RMC. From the 100-amp breaker in the cutoff panel, the hot wires connect to the subpanel bus, the neutral wire to the neutral bar, and ground wire (which is attached to the neutral bar in the cutoff panel) to an unbonded ground bar that has a dedicated ground rod. The heater and workshop grounds are connected to the ground bar. Nothing is connected to the neutral bar except the cable from the cutoff panel neutral bar.
First off, does this sound as if it is properly wired? I know that the NEC states that, in a subpanel, neutrals and ground wires should be isolated. But as I described, are they really? Because the neutral wire and ground wire share the same neutral bar in the cutoff panel and, because the ground wire in the subpanel is connected to that same neutral bar in the cutoff panel, the ground wires in the subpanel are indirectly (through the ground cable) connected to the neutral bar in the cutoff panel. In other words, how can the ground wires be considered to be isolated from the neutrals?
Secondly, can we assume there are three grounds: one rod to the subpanel (which I can see), one rod/RMC to the cutoff panel (which I can see and appears to be an RMC ground), and one rod/RMC to the house panel (which I cannot see because I have limited access under the house)? BUT, if the cutoff panel has a dedicated ground (rod/RMC), why does the sub panel need its dedicated ground rod if its ground bar is already grounded via the cable from it to the cutoff neutral bar - that has its own ground wire attached?
My web searches have not discussed my scenario and, therefore, I would appreciate it if someone could enlighten me, in general, regarding isolating grounds from neutrals (when they seem to be indirectly bonded) and, specifically, the appropriateness of my panels as wired.
Thanks, Monk
Old 11-21-20, 09:55 AM
pcboss's Avatar
Received 180 Upvotes on 158 Posts
The neutrals and grounds are bonded at the first means of disconnect past the meter. After that they should be separated. Detached structures would also require a grounding system.
I am not seeing any issue the way you described.
Ground rods are for high voltage events like lightning or surges. Entirely different purpose than the grounding of a receptacle.
HMonk09 voted this post useful.
Old 11-21-20, 10:00 AM
H
Many thanks PCBOSS for your instant and satisfying response..