Sub panel install - redundant breaker?

If both my panels have a 100A main breaker, do I really need another 100A breaker in the main panel to feed the subpanel or can I connect directly to the panel somehow?

The main panel does not have any other breakers in it, all of them are in the sub panel....

Thanks a

gain!
 

Popular Reply

 
11-22-20, 02:51 PM
pattenp
pattenp is offline
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
Not unless the panel has feed through lugs.
 
  #2  
Old 11-22-20, 02:51 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
Not unless the panel has feed through lugs.
 
C-COOP, CasualJoe voted this post useful.
  #3  
Old 11-22-20, 03:49 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,808
Received 253 Votes on 221 Posts
The only way to connect the wires to the main panel is with feed-through lugs as Pattenp mentioned, or from a breaker. You may not put two wires under a single lug.

If the sub-panel is in the same building it does not require a main breaker, you may use an MLO (Main Lug Only) panel.
 
C-COOP voted this post useful.
  #4  
Old 11-23-20, 03:09 PM
C
Member
Thread Starter
Join Date: Apr 2004
Location: Calgary, Canada
Posts: 435
Received 0 Votes on 0 Posts
So there does seem to be some feed-through lugs on this old panel. It looks like the garage subpanel is already attached to them. Can I also put another subpanel on to the same lugs together with the garage panel feed?
I have attached a picture of both lugs - one above the breakers and one below the breakers....


 
  #5  
Old 11-23-20, 04:47 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,808
Received 253 Votes on 221 Posts
Can I also put another subpanel on to the same lugs together with the garage panel feed?
No, and those garage wires should not be there either. First off I highly doubt that those lugs are designed for more than one wire. Second, those wires are much smaller than the wires feeding the panel and are likely overfused, if fused at all. This needs to be corrected right away!

If you post a picture of the entire panel we can make suggestions to properly wire your panel.
 
  #6  
Old 11-23-20, 04:59 PM
C
Member
Thread Starter
Join Date: Apr 2004
Location: Calgary, Canada
Posts: 435
Received 0 Votes on 0 Posts
Hmmm... well it has been like that since the 60's I am guessing. The feed wire from the breaker is much heavier gauge than what goes to the garage (my pics aren't that good....
 
  #7  
Old 11-24-20, 12:50 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,765
Received 97 Votes on 87 Posts
Your main panel.....is that a Federal Pacific or Federal Pioneer panel? I believe it is so my suggestion is to replace it with a larger panel that does have feed-thru lugs. I think I would replace it with a Square D QO panel.
 
 